  1. Cornell3786 New Member

    joined: Sep 5, 2012
    17 posts
    Roscommon, Mi
    I am working on the last piece of my Econoburn 150 boiler install, and I never put any thought into this, thinking it would be a no-brain er.

    The wiring diagram does not make sense to me. The terminals on the Aqua stat are not labeled.
    The white piece of paper describes the circuit panel on the back of my boiler.

    2012-11-05_10-27-31_31.jpg 2012-11-05_10-28-02_733.jpg Picture 6.png

    Could someone help simplify??
    #1

    Helpful Sponsor Ads!



  2. avc8130 Minister of Fire

    What is the aquastat supposed to do? The L4006A is a Break On Rise aquastat. The 2 terminals will be connected until the water temp reaches the set point of the aquastat. Generally this is used as the boiler over temp control.

    ac
  3. Cornell3786 New Member

    joined: Sep 5, 2012
    17 posts
    Roscommon, Mi
    I got hosed by my boiler dealer. I was supposed to by sent everything I would need for the install. He sent me one pump, almost no parts, 1" underground pipe(later to find its way undersized) and this aquastat. Also wanted me to plumb this in without a near boiler loop.

    To be honest I dont know what it is supposed to do. I thought it communicated with the blower, turning it on and off depending on water temp.
  4. avc8130 Minister of Fire

    It might be the control aquastat. I don't have an Econoburn so I'm not 100% sure. Since it is a break on rise, it could be used for the draft fan. Set to 180 it would "break" when the water temp hits 180 and "make" when the water temp drops below the differential setting. My Wood Gun uses a L4006A for this function.

    ac
  5. Cornell3786 New Member

    joined: Sep 5, 2012
    17 posts
    Roscommon, Mi
    That sounds like it would work.

    So it shouldn't matter what wire is on what terminal when the temp gets to whatever I set it to it will break and turn the fan off.
  6. maple1 Minister of Fire

    joined: Sep 15, 2011
    1,947 posts
    Nova Scotia
    It's just a simple on/off switch, more or less.

    Line in on one side (black power wire), then line out to blower on the other (also black) - wire nut the whites together inside the enclosure.

    My guess.
  7. avc8130 Minister of Fire

    Correct.

    ac
  8. Cornell3786 New Member

    joined: Sep 5, 2012
    17 posts
    Roscommon, Mi
    Thanks guys I've learned a ton from everyone here! Much appreciated
  9. goosegunner Minister of Fire

    joined: Oct 15, 2009
    1,078 posts
    WI
    Did you get the documentation with the boiler?

    PDF documents available on Econoburn site under resources.

    My Econoburn controller has terminals for the aqustat. It is a safety that shutsdown the fan if there is a overheat. The controller also does that at setpoint, this is extra.



    Are you using storage? If so their recommended bypass loop is adequate for return protection, install a Danfoss or similar.