    I'm planning on getting the Englander/Summer's Heat 13-NC. The installation manual says that it requires an R value of '2'. I calculate that, using cement board alone, I would need stack eight 1/2" sheets to achieve that R rating. Assuming I need to put thinset between each layer and I need to wait 24-hours for the thinset to cure before putting on the next layer, this will take up to 8 calendar days!!!

    Is there anyway to build it faster? Can I skip letting the thinset cure between layers? - or can I skip the thinset between all but the top/bottom layers?

    PS: as a side question, do people like the 13-NC around here?

    Thanks!
    #1

    Helpful Sponsor Ads!



  2. mellow Minister of Fire

    joined: Jan 19, 2008
    1,756 posts
    Salisbury, MD
  3. bag of hammers Minister of Fire

    joined: Jan 7, 2010
    603 posts
    Northern ON
    depending on how elevated you want / need your hearth to be, maybe you have other / better options IMHO. For example, if it were me, I would think about maybe building up a couple inches using metal furring strips or studs, set on narrow centers (for lots of support), with roxul or similar fill in all the spaces - a sort of framed / insulated hearth pad. Just thinking out loud (I only needed ember protection so I have durock over plywood for a base, with tiles on top of that). If I recall, there are also other insulating materials that have been discussed here (Micore?).
  4. ddahlgren Feeling the Heat

    joined: Apr 18, 2011
    312 posts
    SE CT
    Sounds like they are tranferring their lack of engineering to your door step..
  5. Highbeam Minister of Fire

    Yeah, it's pretty lame to have to build this much R-value into your hearth. I had to get a 1.2 for my heritage and it sucked. Ended up using an "air space" made by building a 3.5" thick box out of steel studs and skinning that with 2 layers of durock and tile.

    As to your question. Since you are using thinset AND screws to hold the layers together, I would not wait for the thinset to cure between layers. The screws are maintaining your gap whether you like it or not. Of course, stagger the seams, use the durock tape and the durock screws. Is your floor stout enough to support all of that weight?
  6. ddahlgren Feeling the Heat

    joined: Apr 18, 2011
    312 posts
    SE CT
    It is more than pretty lame it is lack of concern for use for the task involved.
  7. raybonz Minister of Fire

    joined: Feb 5, 2008
    5,994 posts
    Carver, MA.
    If memory serves me correct Durock NexGen has an R-value of .39 per 1/2" so 5 sheets is pretty close but to be extra safe you need 6 sheets.. If you decide to build with the Durock make sure you thinset between all layers and the subfloor and stagger your seams if you will have seams.. The hearth requirements of the NC-13 are ridiculous Englander should address this issue.. I wouldn't buy a stove that requires such a high value as there are many stoves that are ember protection only with no R value requirements or a very low R value that's easily achieved..

    Good Luck,
    Ray
  8. TheBaron New Member

    joined: Dec 27, 2012
    78 posts
    Eastern ON, Canada
    Mine required R2.9 I believe. We used Micore (2 layers), then two layers of Durock.

    Screwed and thinset between each layer. Drier mix than usual as the Micore absorbs some water.

    Some folks on here recommend against putting thinset against Micore however the contractor installing mine did not share that opinion. Likely good advice if you have a very flat surface you are mating to.
  9. begreen Super Moderator

    joined: Nov 18, 2005
    36,134 posts
    South Puget Sound, WA
    Use no thinset for the micore layer, just screw through the Durock to hold it captive. If you use Micore 300 it will give you R=1.03 for a 1/2" thick sheet, but if you can get Micore 160 it goes up to R=1.27. Add a couple layers of Durock Next Gen on top of 1/2" Micore 160 and you have a sandwich value of R=2.05.
  10. Highbeam Minister of Fire

    I was unable to source micore in my area. If you can find it then that will make life mch easier.
  11. Jon1270 Minister of Fire

    joined: Aug 25, 2012
    575 posts
    Pittsburgh, PA
  12. morphic New Member

    joined: Feb 14, 2013
    3 posts
    Thanks everyone for the quick replies!

    At first I was discouraged to get micore because I couldn't find it in my area, but I see I can order it online - four 2'x4' 1/2 sheets of 300 (not 160) for $95.50 from Sears for $100.29 ($95 + $0.01 S/H + $4.78 tax), which is about $10 cheaper than anywhere else. Here's the link to it: Drolet Micore-300 Mineral Fiber Board 48" X 24", 4-Pack. Stacking two layers, I'd have 48"x48" @ R=2.06. With that, I don't need any more insulation, but would still need a CBU, so one layer of 1/2" durock. I'd need two sheets to cover 48"x48", which would be about $20, so all said, about $120 for R2.32 in 1.5". Using 8 layers of Durock, I would've needed a total of 10 sheets, which would be about $101 (inc. tax) for R2.08 in 4" - so the micore solution is $19 more expensive but 2.5" less thick! Then there's the weight. The all-durock solution would be 324 pounds, where the micore solution would be just 74 pounds (249 pounds less!). Using micore is totally worth it :)

    Thanks again!
  13. morphic New Member

    joined: Feb 14, 2013
    3 posts

    So what's the prevailing forum wisdom? Is thinset needed between any of the following layers in my stack?
    • micore-durock (tiling surface)
    • micore-micore (insulation layer)
    • plywood-micore (base)
    Of coarse I'll use thinset on top of the durock for the tiles, it's the other layers I'm unsure about...
  14. KaptJaq Minister of Fire

    joined: Jan 31, 2011
    555 posts
    Long Island, NY
    I would not put thinset on the micor layers. USG data sheets show that micor absorbs the water from the thinset and that affects its properties. I personally would not put thinset anywhere except between the tiles and the cement board. Use screws to connect the other layers.

    KaptJaq
  15. Jon1270 Minister of Fire

    joined: Aug 25, 2012
    575 posts
    Pittsburgh, PA
    Thinset between substrate layers is there to fill in irregularities, not for adhesion. In most tile work, which doesn't use Micore, thinset forgives a lot of sins. But Micore is, according to the manufacturer, not tolerant of moisture. When I built my hearth, I made up for the absence of thinset by being perfectionist about the flatness of all the mating surfaces, and by torquing all the fasteners very consistently using a rechargeable drill's torque adjustment. It's only been a few months, but the tile job looks great so far.
  16. tekguy Burning Hunk

    joined: Nov 12, 2009
    119 posts
    west mass
    i ended up getting it for free... its used in partition walls for office furniture like at any large company, I lucked out and got partition walls that where going to be trashed and pulled Micore 300 sheets out of the middle
  17. EatenByLimestone Minister of Fire

    joined: Jul 12, 2006
    4,114 posts
    One hearth I built used micore. I stacked 2 layers and screwed them down using plaster washers. Hardie board went down next and was screwed down. Then came a layer of thinset and the tile.

    Another one was for a cabin. I just stacked 3 layers of Durock next gen. They aren't even screwed down, but the wife has not told me how she wants it to be finished. I'll make it pretty after the boss gives me her instructions.

    Matt