Insulating a Expansion Tank

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

sdrobertson

Minister of Fire
Hearth Supporter
Aug 13, 2007
735
West Michigan
Could someone post the formula to figure out how many gallons of water will move into an expansion tank. I have 2000 pressurized gallons and I need to know how many gallons of water will move to and from the expansion tank and how fast from 130 degrees to 180 degrees. My expansion tank is in a insulated boiler room and I don't really want to insulate the tank itself as I have to be able to see the gauge, so if it isn't allot of water, I'll just live with the heat loss.
 
You can find this on Google. Precise answer is pretty close to 4%, and varies depending on start and end temps. I tend to use 5% as a rule of thumb, which comes pretty close to 50-200 range.
 
Status