    My shop has a masonry chimney (chimney block with clay liner) installed on the inside wall. The existing construction has OSB wall what butt flush with the chimney, as does the ceiling. I'm about to blow in cellulose in the ceiling and it dawned upon me that I might have some clearance issues.

    Is the OSB on the walls or ceiling a concern? If so that's a hard fix.

    Any issue with cellulose in direct contact with the masonry. I can build a barrier to maintain clearance but it is cramped for space and I don't want to mess with it if it's not a concern.
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,204
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    I don't know code here, but I thought the chimney was supposed to have a 1" (?) clearance from combustibles.
     
    Collapse Signature Expand Signature
  3. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,012
    Likes Received:
    1,394
    Loc:
    Indiana
    A 1" clearance is required by code for Masonry chimneys.
    This clearance is rarely met in most houses though. It's rarely an issue, the few times that this was an issue, well, went up in smoke!;)

    I put a liner in a 30" wide chimney that had a flue fire a few days before I got there. Vinyl siding touched the edges of the block flue, and it was all warped and buckled from the heat the entire length of the chimney. It's pretty scary, keep an inch around that chimney!
     
    Collapse Signature Expand Signature
  4. Pallet Pete

    Pallet Pete
    Expand Collapse
    Guest

    It varies by county much of the time ours is 2" requirement most of the surrounding are 1". It may be worth calling the stove inspector to find out for sure. Normally it's the mechanical inspectors department you call.

    Pete
     
  5. lukem

    lukem
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 12, 2010
    Messages:
    3,687
    Likes Received:
    1,518
    Loc:
    Indiana
    Ha! We barely have permits let alone inspectors. If I'm going to honor the 1" I am looking at full tear out because the outsidebwall is completely touching it. I'll pull back some of the OSB on the wall and see if they left a gap in the structure. Judging by the rest of the poor construction I'm guessing not.
     
    Collapse Signature Expand Signature
    Pallet Pete likes this.
  6. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,012
    Likes Received:
    1,394
    Loc:
    Indiana
    The 1" clearance is an IIRC and NFPA code. I don't see how a certain county could require more than International codes requires.
     
    Collapse Signature Expand Signature
  7. Pallet Pete

    Pallet Pete
    Expand Collapse
    Guest

    I have no idea as to why What is this wood burners against down drafters alliance ? That sounds like its right up my alley lol.

    Pete
     
  8. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,012
    Likes Received:
    1,394
    Loc:
    Indiana
    Oh, just professing my deep hatred for down drafters after my experience with a Lopi Leyden.
     
    Collapse Signature Expand Signature
    Pallet Pete likes this.
  9. Pallet Pete

    Pallet Pete
    Expand Collapse
    Guest

    Well I might just join you after my Harmon experience lol. Now back to your regularly scheduled thread !

    Pete
     
  10. tfdchief

    tfdchief
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 24, 2009
    Messages:
    3,336
    Likes Received:
    1,295
    Loc:
    Tuscola, IL
    Generally, you need 2 in. clearance to combustibles.
     