Is nothing easy??? Time to switch gears

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by suprz, Oct 13, 2012.

  1. suprz

    suprz Member

    Joined:
    Sep 24, 2012
    Messages:
    219
    Loc:
    Rhode island
    Ok well, after much research...i have more questions! The minimum hearth pad size for my stove is 43 deep by 38 wide. And the back of the stove has to be 17 inches from a combustible. (Wall in this case) the max that we can have this stove protrude into the room is 43 inches. If it comes out at 50 inches it is a deal breaker and i will have to scrap the idea of a woodstove. Now my stove has a rear heat shield and we were only going to build a hearth pad, but i spoke to the guys putting in my chimney and he said that if i put durock and tiles on the wall with a 1 inch air gap behind it, i can get closer to the wall than the 17 quoted in the manual because it is not considered a combustible now. Is that true? Cause if it is i can finally have my wood stove!!! I wouldnt go closer than 8 inches, and the black pipe is going to be double walled so that shouldnt be an issue

    What do you experts say??

    Helpful Sponsor Ads!





  2. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,446
    Loc:
    Bend, OR
    If, and only if, the appliance manufacturer specifically states in the owner/installation documentation that the rear clearance to combustibles as shown in the manual installation tables/diagrams may be reduced by the use of an approved wall shield can this method be used. If the book says you can do it, then we can guide you through it. Rick
    ScotO and DAKSY like this.
  3. suprz

    suprz Member

    Joined:
    Sep 24, 2012
    Messages:
    219
    Loc:
    Rhode island
    The maual says that different manufacturers produce accessories that will alow reduced clearances that the testing jotul has put forth in the manual and that there are also N.F.P.A.211 code to consider if you wish to build your own wall and floor protection. so... They dont say i cant, and dont say i can....
  4. gmule

    gmule Feeling the Heat

    Joined:
    Feb 9, 2011
    Messages:
    452
    Loc:
    Conifer Colorado
    I'm no lawyer but the first sentence tells me that it is okay.
    ScotO likes this.
  5. ScotO

    ScotO Guest

    Looks like a call to Jotul may be in order. Maybe they can give you a definate answer regarding the supplementary heat shield. I would think you should be fine, that is what those supplementary shields are for......but you wanna cover all the bases prior to commiting to the project.
  6. Stump_Branch

    Stump_Branch Minister of Fire

    Joined:
    Nov 12, 2010
    Messages:
    878
    Loc:
    MD
    Do a but more research here. You'll find how to build that rights hearth. Meaning what makes a combustible wall. With the proper air space installer is correct. However,mentioned above find the manual. Don't build something unsafe.

    Welcome, and good luck.
  7. rwhite

    rwhite Minister of Fire

    Joined:
    Nov 8, 2011
    Messages:
    621
    Loc:
    SW Idaho
    It seems that the 43x38 minimun pad size assumes that the pad will sit 9" away from the wall. If you want the pad all the way against the wall by the manual The pad will have to be 52x38, but the actual stove front will only be at 34" from the wall (if my math is correct the stove is 17" deep?) . So by building an air gap you want to reduce the rear clearance to 9". I doubt that you'd get buy off from Jotul to do that. Mainly because they have know way to know what your construction will consist of and no way to test it. Manufacturers only have the ability to test their product against a standard install. It would be near impossible to test every install scenario that people come up with and I doubt they would assume the liability that your construction is done right. I would post some pics of the install area and see if anyone has any ideas. One may be that the pad is built flush with the floor to prevent a trip hazard. and that would provide the proper clearances and still have the stove front at 34" away from the wall. Manual states that the floor protection must be 3/8 non-combustable mill board so the floor could be cut out to accomodate that.
  8. SteveKG

    SteveKG Minister of Fire

    Joined:
    Jun 23, 2009
    Messages:
    590
    Loc:
    Colorado Rockies
    Not an expert, just someone who's lived with several wood stoves for decades. I have one of our stoves in a room which, due to the layout and stairwell, the stove can only work near one wall. I need that stove; it heats the back half of our cottage. So, I have the stove about seven inches or so from the drywall wall. What I did was build a double heat shield of heavy-gauge sheet metal. In other words, from the wall outward, I have drywall, then an air space, then the shield, then another air space, then another shield. It's been this way for 25 yr. or so, and the drywall never gets hot. I measured the temp. last year, and I don't recall what it was, but I do know I chuckled and felt good. It was barely warmer than room temp, if that. I have heard of folks putting a triple-shield up, but in my case, it isn't necessary.

    So, there are options. I cannot speak to what a manufacturer would say.
  9. begreen

    begreen Mooderator Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    49,170
    Loc:
    South Puget Sound, WA