Overheat loop design

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by mmudd, Nov 29, 2012.

  1. mmudd

    mmudd
    Expand Collapse
    Member

    Joined:
    Jun 7, 2012
    Messages:
    78
    Likes Received:
    8
    Loc:
    Central MO
    I am getting ready to complete my overheat loop. Question on the layout. Most seem to be fin tube oriented horizontally up above the boiler. I was wondering if a vertcal layout such as shown (see crude drawing) using 3/4 fin tube and 1" manifold, supply & return would work or would it be much less effective in dissipation of heat and just another one of my half baked ideas.
     

    Attached Files:

    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. mikefrommaine

    mikefrommaine
    Expand Collapse
    Guest

    I think with that layout most of the water would go up the left vertical header and across the top piece of finned copper. The lower pieces of finned copper would not see much flow.
     
  3. maple1

    maple1
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 15, 2011
    Messages:
    6,372
    Likes Received:
    1,103
    Loc:
    Nova Scotia
    Mike, I think you were looking at it sideways - maybe?

    The water would likely flow through that arrangement OK - but fintube isn't designed to radiate heat oriented vertically. It would still likely dissipate heat, but I'm not sure it would dissipate much more than bare copper. Well, it likely would, but not near what it would horizontally inside its shell - which is another point, running fintube without it being inside it's cabinet/shell also reduces directed air flow & heat transfer.
     
    Collapse Signature Expand Signature
  4. mmudd

    mmudd
    Expand Collapse
    Member

    Joined:
    Jun 7, 2012
    Messages:
    78
    Likes Received:
    8
    Loc:
    Central MO
    Thanks Mike, you must have looked at it sideways. Cause the fin tube runs vertical in the example. I wondered if the dissapation would be diminished in a vertical arrangement.
     
    Collapse Signature Expand Signature
  5. Fred61

    Fred61
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 26, 2008
    Messages:
    2,012
    Likes Received:
    385
    Loc:
    Southeastern Vt.
    Of course! The fin tube is like a pump. Air between the fins becomes lower density, rises and is replaced by colder air from below the fin tube etc, etc, etc. You would not be utilizing the full fin if mounted horizontally plus heat from the lower fin would be warmer than room air and wouldn't absorb as much heat. The baseboard housing adds some efficiency to them but they work very well without it. Don't hang the tubes tight to the ceiling!
     
    Collapse Signature Expand Signature
  6. mikefrommaine

    mikefrommaine
    Expand Collapse
    Guest

    Yep just looked at it again, it opens sideways on my iPad. Should have noticed the writing was sideways too.

    I too would be concerned about diminished output due to decreased air flow. Though I'm not sure it would make a big difference. I have not noticed a strong air flow across my overheat loop that is the more traditionally oriented ceiling mount.

    I'm going to go kill the power to my boiler to see how much air flow is developed
     