PE Vista Blower issues

Walter Posted By Walter, Nov 14, 2012 at 2:00 PM

  1. Walter

    Walter
    New Member 2.
    NULL
    

    Nov 14, 2012
    3
    0
    I have a 5yearold PE Vista C Wood Insert. The Fan(blower) turns on and works when I switch it to ON. But in "AUTO" mode will not come on. Is there something I can replace or check? The Installer wants 150$ just to come look at it So Im trying to save money here.
     
  2. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,606
    7,878
    Loc:
    South Puget Sound, WA
    It sounds like the snap switch may have given up. This should be pretty simple to fix. You'll need to pull off the back heat shield, remove the old snap switch and replace it with a new one of the same rating/values. A new snap switch should be under $15.
     
  3. Walter

    Walter
    New Member 2.
    NULL
    

    Nov 14, 2012
    3
    0
    That's what I thought. I pulled the front blower assembly off (2 screws ya!) and saw that part. I figured it was some sort of thermostat. According to the manual This is the part

    Problem is I don't know what the rating is. Would be it listed in the manual? I have that here. https://docs.google.com/document/pub?id=1PbqeaEO6Uw4KVW0NNWGyAnDZwVv5lLTagQdIC_DtABE
     
  4. Walter

    Walter
    New Member 2.
    NULL
    

    Nov 14, 2012
    3
    0
    Just an Update. After pulling the blower assembly off. I just did a quick cleaning while I was in there. Tonight when I started the Fire. It turned on on its own! Guess I needed a good cleaning.
     