Pellet Liner Flex Kit

titikiki Posted By titikiki, Jul 4, 2008 at 3:33 AM

Thread Status:
Not open for further replies.
  1. titikiki

    titikiki
    New Member 2.
    NULL
    

    Jun 21, 2008
    17
    0
    Loc:
    Calverton, NY
    With the help from advice on this forum I placed an order for the Mt Vernon Quadrafire Insert. The dealer stated that my present metal insert and piping would have to all come out. For venting up my wood chase he ordered 25' 3" Pellet Liner Flex Kit (Duravent). I had read on another posting here that flex can not be used with a wood chase. Is my dealer steering me wrong or is this actually a safe and correct option for the Mt Vernon? Thanks for any opinions. Happy 4th!
     
  2. stoveguy13

    stoveguy13
    Minister of Fire 2.
    NULL
    

    Dec 15, 2006
    984
    27
    Loc:
    CT
    you can not use flex inside a wood chase only in masonary you will need to run rigid pipe
     
  3. jtp10181

    jtp10181
    Minister of Fire 2.
    NULL
    

    Feb 26, 2007
    3,729
    3
    Loc:
    Madison, WI
    Unless he is leaving the old ZC wood unit in there and running the flex up the old pipe? But if everything is coming out as he said you cannot use flex inside the wood chase, it must be rigid type L or pellet pipe.
     