Radiant floor retrofit - adding extra mass? advice?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

scottinkn

Member
Hearth Supporter
Oct 12, 2008
50
Monson, MA
www.servu724.com
Hello everyone I am about to retrofit radiant floor underneath 3/4" subfloor with 1/2" PEX AL PEX. mixed floor coverings on 1st floor...

Joists are 16" on center and I will run 2 pipes in each bay 6-8 inches apart.

My current system is baseboard hotwater... cheap baseboards and my entire system is undersized it had never really kept the house warm (When it was oil fired) on single digit days. so we got a wood stove and then later indoor wood boiler in series with oil & 1000 gal tank

So my retrofit is add on

I want to improve efficiency of system (inexpensively) and lower water temps to get more out of my 1000 gals of storage because I dont really get any heat from baseboards when the temp is under 160.

I am hoping the warm floor is going to change all that!

So here I am, about to pull pipe through the holes that I have drilled for 4 zones 225' - 250' each from where the manifold will be,
I am thinking about plates and floor mass. i know that tile, wood & carpet all will effect temps and response times. If i were to add more mass, say extra plates or foil covered sheet rock in between the pex runs(as a spacer) then maybe even foil then sheetrock over that. or how about even using aluminum foil and covering the joists?
Are these ideas stupid?
Am I crazy or would more mass be better?
 
I used Thermofin C and 1/2 inch Pex in my retrofit. 3/4 inch osb subfloor, hardwood and tile finish floor.
I used an angle grinder to cut all the hardwood floor nails off flush with the underside of the subfloor.
I used an inexpensive 1/4 inch impact driver and self piercing #8 x3/4 screws to secure the Thermofin.
Drilled holes near the joist end, pulled pex, banged in place in Thermofin with a rubber mallet.
4 runs, 350' (equalized) each. Constant circulation, outdoor reset.

The floor is not cold, but doesn't really feel warm until it is -10 F outside. It delivers 100% of the heat needed on the first floor with an indoor design temperature of 68 F and an outdoor design temperature of -20 F, a maximum water temperature of 145 F, and a maximum calculated floor surface temperature of 85 F. It kept up fine last year with temperatures colder than that.

I am glad I spent the money.

I would caution you regarding PAP over pex. I am absolutely certain I would not have had success pulling 300 foot loops through holes in the joists, bending over and around existing plumbing, wiring, reaching the joist end, going back, and doing it again (and again and again ...) without kinks every five feet. I did not have a problem with pex kinking, except for twice, both of which I was not paying attention to what I was doing.

The Uponor Complete Design Assistance Manual is an excellent reference, available in PDF download for free.
Zurn and Viega have good reference manuals as well.
Start there with a heat loss calculation, then figure your btu per square foot delivery with different underfloor methods and different water temperatures.

Uponor / Wirsbo have Joist Trak, similar to Thermofin
There are also lots of light gauge plates available.




ETA, I have heavy aluminum plates, but additional (lack of) mass has not mattered in my case. The outdoor reset varies the water temperature, and the floor is responsive. We don't overheat when a clear 20F fall night turns into a nice sunny 50F fall day.

Panel radiators were mentioned below, and replacing some or all of the baseboard may be easier and possibly less expensive than the floor retrofit. I installed Buderus panel rads on my second floor, one in each room, sized to provide all the heat needed with the same temperature water as the floor retrofit. A thermostatic radiator valve on each, a Grundfos Alpha pump, and nice even heat all the time.

Before you do anything, do the heat loss calculation, figure out how many additional BTU per square foot you need to supply in your different areas, look at your floor R values, and see if that energy can be delivered with your desired water temperature if you have heavy, thin, or no heat transfer plates.
 
Last edited:
  • Like
Reactions: BoilerMan
I would also advise not to use PAP as it's a bear to pull through lotsa joist holes. Use a quality PEX-a such as Wirsbo/Uponor hepex, or Mr.Pex O2 barrier. PEX-a is softer (read more pliable) and makes this type of job easier. Calculate your loop length and start in the middle of the run so you only end up pulling about 150' each way back to manifold. The plates are the best dry system thermo-transfer.

Radiant systems, lowest temp to highest:

1. Radiant slab (tubing embedded in thick concrete)
2. Thin slab/gypcrete pour-over (tubing in slab poured-over wood subfloor)
3. Below wood subfloor with thick transfer plates, insulation below plates
4. Stapled up tubing directly to subfloor with insulation below
5. Stapled up system with no insulation below

EDIT: There are also products that sandwich the tubing on top of the subfloor with flooring directly on top of that such as Warmboard etc.

TS
 
An alternate plan would be to use wall hung radiant panels.
As mentioned, staple up systems require higher water temperatures, so as it gets colder out, your storage temps will have to be higher and/or you are going to be doing more firings to keep temps up.
It is worthwhile to do a heat load calculation and then compare that against panel or floor performance to see what the lowest temperatures are that you can keep some reasonable comfort.
Pencil and paper are free.
 
Yep, do the heatloss calculation first and foremost. Any well designed heating system starts here.

Your on the right track with the low supply temps to maximize storage. It's a beautiful thing. With staple up I don't see making this happen without extruded plates-$$$. Panel rads with TRVs, sized for low temps, could start looking pretty good.

Another vote for constant circulation and ODR, whether panel rads or staple up. It's awesome.
I designed for 120 deg F supply at design temp and at avg temps I am around 105deg F. I fire every other day in avg temps. The convenience is worth the price of admittance for me.

Of course you won't know what to expect without that load calc. Figuring your areas and assigning the correct R value will take more time than crunching the btu/hr numbers.

Noah
 
I made my own hybrid system over my concrete floor. The basement had baseboard heat. I developed a leak somewhere in the floor and decided this was easier then to start cutting concrete looking for it. I layed foil down under the plywood and tapcon the wood to the concrete. Then i routed all the groves keeping each loop less then 250ft i did 6" or 8" centers. Then wrapped it loop in a u shape of foil and put engineered floating floor over top. I did this 5 or 6 years ago. The system works great it was a lot of work but worth it in my option. It is not as good as concrete based in floor but with the built in dressers i could not raise the floor height with concrete.

Radiant floor retrofit - adding extra mass? advice?
 
A good controller, with outdoor reset, running a mixing valve to vary the temperature to the pex circuits according to demand would cost a lot less than a thin slab and probably work better.

Just my intuitive take on it.
 
  • Like
Reactions: arbutus
Given that you already have 1,000 gallons of thermal storage (mass), you likely won't see a lot of benefit from adding additional thermal mass to the floor. But you will experience some of the disadvantages of a high-mass floor such as the slow response time and the difficulty in controlling temperature as the demand changes (say the sun comes out and warms the space, or you start cooking in the kitchen which quickly adds a bunch of heat to the space).

You already have the piping for the baseboards throughout the house - I'd suggest swapping out the baseboards for panels sized to deliver the necessary BTUs at a relatively low temp (<140) so you can more fully extract the available BTUs in your thermal storage. That will likely cost less, you can implement it a lot faster and easier, and you'll have the ability to fine-tune temperatures on a room-by-room basis.
 
Hello everyone I am about to retrofit radiant floor underneath 3/4" subfloor with 1/2" PEX AL PEX. mixed floor coverings on 1st floor...

Joists are 16" on center and I will run 2 pipes in each bay 6-8 inches apart.

My current system is baseboard hotwater... cheap baseboards and my entire system is undersized it had never really kept the house warm (When it was oil fired) on single digit days. so we got a wood stove and then later indoor wood boiler in series with oil & 1000 gal tank

So my retrofit is add on

I want to improve efficiency of system (inexpensively) and lower water temps to get more out of my 1000 gals of storage because I dont really get any heat from baseboards when the temp is under 160.

I am hoping the warm floor is going to change all that!

So here I am, about to pull pipe through the holes that I have drilled for 4 zones 225' - 250' each from where the manifold will be,
I am thinking about plates and floor mass. i know that tile, wood & carpet all will effect temps and response times. If i were to add more mass, say extra plates or foil covered sheet rock in between the pex runs(as a spacer) then maybe even foil then sheetrock over that. or how about even using aluminum foil and covering the joists?
Are these ideas stupid?
Am I crazy or would more mass be better?

Some notes about my install: The 1/2" Pex Al Pex wasn't that hard to run at all.I should have went with 3/4" like I originally wanted to. The trick is just make big loops. I would drag a loop about 12 - 15' then shape it starting from where it feeds both sides and make like threading a needle.over main to the other side then feed the slack to the end. I wound up with 4 loops 260' longest and 230' the shortest loop. used a whole 1000' roll of it on 1 floor. my house is 24 x 40 footprint. I started to use sharkbite clips to hold it up (I only used 1 pack) and found that a nail holds up just as good & it was easier than banging overhead clips. As it stands now the system is completely silent and works well. Better than my regular baseboards already and I haven't even put plates or insulated yet. My cellar is 70 - 80 degrees now and upstairs has stayed 62 - 66. I broke my thermometer while working around the tank and I am waiting on replacement. I haven't even gotten my tank up to temp yet....
 

Attachments

  • Radiant floor retrofit - adding extra mass? advice?
    PIC_0006.JPG
    156.6 KB · Views: 260
Now I want to talk about plating it. I don't want to spend a ton and I want to get the most bang for my buck. I priced flashing & to cover it all would be too expensive & I want to try new things so...I plan to staple 12" Aluminum foil in the bays up against the floor, slip the pipes back under the nail, then staple Aluminum window screen over the pipes the entire length of the bay and then foil over (maybe even a few times) that so I have a 1/2" foil air pocket. then 2" foil insulation board over the whole thing spaced at 4" from the floor....
 
As I recall, the commercial staple-up floor systems have a channel that the pex pops into, so a large percentage of the tubing is in contact with the aluminum. I wonder if it would make sense to wrap foil all the way around your tubing before stapling it up in order to suck more heat out of the tubing by conduction? Then proceed with the rest of your plan, which looks like a winner to me.
 