Re-Post Water storage system

sparke Posted By sparke, Feb 4, 2008 at 3:47 PM

Thread Status:
Not open for further replies.
  1. sparke

    sparke
    Minister of Fire 2.
    NULL
    

    Jul 6, 2006
    564
    1
    Loc:
    Maine
  2. Eric Johnson

    Eric Johnson
    Mod Emeritus 2.
    NULL
    

    Nov 18, 2005
    5,875
    147
    Loc:
    Central NYS
    Neat stuff. Nice looking Atmos gasifiers.
     
  3. Bob Rohr

    Bob Rohr
    Minister of Fire 2.
    NULL
    

    Jan 9, 2008
    1,050
    159
    Loc:
    SW Missouri
    Nice looking work. Great planning and layout.

    A classic example of how a 3 way thermostatic can severly constipate a piping system.

    A TACO 007 can easily move 150,000 BTU/ hr at 5 feet of head loss, plenty for that boiler requirement. The reason he had to install a grossly over sized high head pump is the Cv or pressure drop through that 3 way. That's a cv of 3 or 3 GPM valve. That piping must scream with velocity noise. Aa 14 GPM 3 way would have been a better choice, less pump and power consumption and the cavitation issues he will soon experience would disappear.

    hr
     
Thread Status:
Not open for further replies.

Share This Page