Replacing Heat n Glo gas fireplace with Harmon Accentra Insert question about the flue

Post in 'The Pellet Mill - Pellet and Multifuel Stoves' started by arpenn, May 16, 2008.

Thread Status:
Not open for further replies.
  1. arpenn

    arpenn
    Expand Collapse
    Member

    Joined:
    May 16, 2008
    Messages:
    18
    Likes Received:
    3
    Loc:
    Southwest Missouri
    As the title indicates I am replacing a built in Zero Clearance Heat n Glo 6000XLT gas fireplace with a Harmon Accentra Insert with Zero Clearance Box. My question is in the flue. My gas fireplace has a direct vent flue that goes up through my roof. The direct vent flue has a inner liner that is 5" and an outer that is 8" (Double Wall) The inner vented the exhaust from the gas fireplace and the outer was the fresh air intake for the fireplace. My question is can I attach the flue from the Pellet stove to the inner 5" of my existing flue, or will I have to run a new 3" or 4" pipe up the existing flue? I am sure this is as clear as mud.

    Thanks,
    Aaron
     

    Helpful Sponsor Ads!





  2. webbie

    webbie
    Expand Collapse
    Seasoned Moderator
    Staff Member

    Joined:
    Nov 17, 2005
    Messages:
    12,190
    Likes Received:
    1,086
    Loc:
    Western Mass.
    Gas vent is not approved for Pellet exhaust. It is aluminum, whereas Class L (Pellet) is stainless steel.

    Furthermore, I'd have questions about even running a single wall pipe up through it unless that was an installation approved in the Harman manual or by the factory engineers (by fax). I have never heard of relining a gas vent for pellets.

    If you wanted to leave the old gas flue in place, you'd probably have to run a double wall pellet vent up the middle of it. Or, remove it and do the same......
     
    Collapse Signature Expand Signature
  3. jtp10181

    jtp10181
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 26, 2007
    Messages:
    3,729
    Likes Received:
    3
    Loc:
    Madison, WI
    Yeah he is right, technically you can't run a single wall flex liner up through a gas vent. It would have clearances and I'm sure it would be fine but technically its not approved. If the run is straight up you could run the normal type L vent up through it.
     
    Collapse Signature Expand Signature