  1. mtaccone New Member

    joined: Jan 18, 2008
    101 posts
    schenectady, NY
    How do I size the heat exchanger? The plenum coming off the air furnace is 18x20 and goes up to a 26x26 Not sure on what to look for in heat exchangers. My gas heat is 70,000 btu ouput if that helps (not enough improperly sized)
    #1

    Helpful Sponsor Ads!



  2. Jersey Bill New Member

    joined: Jan 21, 2008
    132 posts
    Central NJ
    For an air system, btuh=1.08 (delta T)(CFM)
    I would guess 50 degree heating delta (120-70)
    so the CFM = 1300 (about), but it could be higher.
  3. leaddog Minister of Fire

    joined: Sep 24, 2007
    912 posts
    Hesperia, Michigan
    get the largest one to fit your opening as you have to make sure you close off any air flow except thru the ex. You want the air flow to not be restricted and not bypass at all. a 18x20 will do it.
    leaddog
  4. eekster New Member

    joined: Oct 24, 2007
    51 posts
    southeast michigan
    I agree with leaddog, don"t go small, I have a 75,000 btu furnace with a 20 x20 exchanger, which I think it is capable of 100,000 btu"s if I"m not mistaken. Go bigger not smaller . Have no problems with a/c due to air flow , and very nice heat.
    Keith
  5. mtaccone New Member

    joined: Jan 18, 2008
    101 posts
    schenectady, NY
    Answered perfectly Wasn't sure about restriction.. My furnace is 88000 btu in and 70,000 out. according to the label.