Zone Valve End Switch not working

machinistbcb Posted By machinistbcb, Oct 21, 2008 at 7:09 PM

Thread Status:
Not open for further replies.
  1. machinistbcb

    machinistbcb
    New Member

    Nov 21, 2007
    109
    0
    Loc:
    Sabattus Maine
    The endswitch on one of my honeywell zone valves model v8043f1036 is not starting my circulator. The valve is opening and closing fine when I turn up and down my thermostat. Any ideas ? how hard is it to change the heads ?? Is there any way that I can jump onto one of my other zone valves to start the circ up with-out opening the valve along with it ?

    Thanks,

    Brian
     
  2. waynecub

    waynecub
    New Member

    Mar 1, 2008
    29
    0
    Loc:
    vermont
    Can you tell me how you have wired it up. Check the end switch wires with a continuity tester. You should have no continuity when the stat is turned down and when the stat is turned up you should have continuity. The end switch has no power, it's only a switch.
    Marcus
     
  3. Nofossil

    Nofossil
    Moderator Emeritus

    Oct 4, 2007
    3,556
    60
    Loc:
    Addison County, Vermont
    Those switches do fail - it's happened to me before. It's actually a standard microswitch and can be replaced if you can find a source.
     