Zone Valve End Switch not working

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by machinistbcb, Oct 21, 2008.

Thread Status:
Not open for further replies.
  1. machinistbcb

    machinistbcb
    Expand Collapse
    New Member

    Joined:
    Nov 21, 2007
    Messages:
    109
    Likes Received:
    0
    Loc:
    Sabattus Maine
    The endswitch on one of my honeywell zone valves model v8043f1036 is not starting my circulator. The valve is opening and closing fine when I turn up and down my thermostat. Any ideas ? how hard is it to change the heads ?? Is there any way that I can jump onto one of my other zone valves to start the circ up with-out opening the valve along with it ?

    Thanks,

    Brian
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. waynecub

    waynecub
    Expand Collapse
    New Member

    Joined:
    Mar 1, 2008
    Messages:
    29
    Likes Received:
    0
    Loc:
    vermont
    Can you tell me how you have wired it up. Check the end switch wires with a continuity tester. You should have no continuity when the stat is turned down and when the stat is turned up you should have continuity. The end switch has no power, it's only a switch.
    Marcus
     
  3. Nofossil

    Nofossil
    Expand Collapse
    Moderator Emeritus

    Joined:
    Oct 4, 2007
    Messages:
    3,553
    Likes Received:
    60
    Loc:
    Addison County, Vermont
    Those switches do fail - it's happened to me before. It's actually a standard microswitch and can be replaced if you can find a source.
     