  1. machinistbcb New Member

    joined: Nov 21, 2007
    109 posts
    Sabattus Maine
    The endswitch on one of my honeywell zone valves model v8043f1036 is not starting my circulator. The valve is opening and closing fine when I turn up and down my thermostat. Any ideas ? how hard is it to change the heads ?? Is there any way that I can jump onto one of my other zone valves to start the circ up with-out opening the valve along with it ?

    Thanks,

    Brian
    #1

    Helpful Sponsor Ads!



  2. waynecub New Member

    joined: Mar 1, 2008
    29 posts
    vermont
    Can you tell me how you have wired it up. Check the end switch wires with a continuity tester. You should have no continuity when the stat is turned down and when the stat is turned up you should have continuity. The end switch has no power, it's only a switch.
    Marcus
  3. Nofossil Minister of Fire

    joined: Oct 4, 2007
    3,279 posts
    Addison County, Vermont
    Those switches do fail - it's happened to me before. It's actually a standard microswitch and can be replaced if you can find a source.