rjAKAmoses

New Member
Dec 13, 2020
2
Wisconsin
Hi, I just started using my 6039 again, after a few years. I know that the A button adjusts the feed auger and the B button adjusts the combustion fan. I have forgotten why two different sets of numbers come up with each when pressing them. EX. I press A, I get 2-5 in the displays, I press A again I get 3-7 in the display. I press B, I get 7-0 in the display and the red light above C comes on, I press B again, I get 0-0 in the display and the red light above B comes on. If I press either a third time it goes back to Heat Range and Blower Fan numbers. Can anyone tell me what those settings would be for? I know there are a few guys on here that swear by these stoves, and even a guy that worked at USSC at some point. Just looking to be as efficient as possible by becoming more informed than the instruction manual can provide.
 
Can anyone tell me what those settings would be for?
Depends on which of the 6 versions of the ABC board you have.

Version 13 b also applies to version 12 b & 11 b
THE A AND B BUTTONS WERE NOT ACTIVE. PRESS THE HEAT RANGE DOWN AND
BLOWER RANGE UP AT THE SAME TIME FOR 5 SECONDS TO ACTIVATE
PRESS THE A BUTTON AND THE HEATRANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE AUGER SETTING. FACTORY SETTING IS 4. THIS CONTROLS
THE AUGER SPEED
PRESS THE B BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE COMBUSTION AIR SETTING. FACTORY SETTING IS 3. THIS
CONTROLS THE COMBUSTION AIR.
RESET TO FACTORY-HOLD IN B & C UNTIL P1 APPEARS. USE THE HEAT RANGE ARROW
INCREASE TO P9 AND PRESS THE ON BUTTON- THE UNIT WILL TURN OFF THE BOARD
WILL BE RESET.

VERSION 32B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THIS VERSION WAS FAMOUS FOR BLOWING FUSES IT CAN ALSO CAUSE THE EXHAUST
AND ROOM BLOWER TO TURN ON AND OFF.
PLEASE TELL THE CUSTOMER WE NEED TO UPDATER THE CONTROL BOARD AND SEND
OUT THE LATEST VERSION TO THEM

VERSION 33 B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THE A AND B BUTTONS SHOULD BE ACTIVE IF NOT PRESS THE HEAT RANGE DOWN AND
BLOWER UP.
THE HEAT RANGE DOWN AND BLOWER SIDE WILL READ THE
AUGER SETTING FACTORY SETTING IS 4 THIS CONTROLS THE AUGER SPEED
PRESS THE A BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE AUGER SETTING FACTORY SETTING IS 4. THIS CONTROLS
THE AUGER SPEED.
PRESS THE B BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE COMBUSTION AIR SETTING. FACTORY SETTING IS 3. THIS
CONTROLS THE COMBUSTION AIR
RESET TO FACTORY- HOLD IN B & C UNTIL P1 APPEARS. USE THE HEAT RANGE ARROW
INCREASE TO P9 AND PRESS THE ON BUTTON- THE UNIT WILL TURN OFF. THE BOARD
WILL BE RESET

VERSION 34 B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THE A AND B BUTTONS WERE NOT ACTIVE. PRESS THE HEAT RANGE DOWN AND
BLOWER RANGE UP AT THE SAME TIME FOR 5 SECONDS TO ACTIVATE. THE A AND B
BUTTONS WILL NOT LIGHT UP WHEN PRESSED
FEED-PRESS THE A BUTTON THE HEAT RANGE NUMER AND BLOWER SPEED NUMBER
SHOULD CHANGE THIS IS THE POUNDS PER HOUR THE AUGER WILL FEED. THE FACTORY
SETTING IS 1.5 THIS IS THE LOW FUEL RATE FOR SETTING NUMBER ONE. DO NOT TELL
THE CUSTOMER THIS IS REFERING TO POUNDS PLEASE REFER TO THIS NUMBER AS
FIFTEEN
FEED-IF YOU PRESS THE A BUTTON TWICE YOU WILL SEE THE HIGH END AUGER SPEED
THE FACTORY SETTING IS 5.0 THIS IS THE AUGER SPEED FOR THE NUMBER 9 SETTING
TO INCREASE OR DECREASE THESE SETTINGS USE THE ROOM BLOWER ARROW UP AND
DOWN
AIR-PRESS THE B BUTTON AND YOU WILL SEE A NUMBER ON THE HEAT RANGE SIDE
AND BLOWER SIDE. THIS IS THE LOW END COMBUSTION BLOWER SPEED (SETTING #1)
THE FACTORY SETTING IS 90
AIR-PRESS THE B BUTTON TWICE AND YOU WILL SEE A NUMBER ON THE HEAT RANGE
SIDE AND BLOWER SIDE. THIS IS THE HIGH END COMBUSTION BLOWER SPEED (SETTING
#9). THE FACTORY SETTING IS 08 WITH C BUTTON LIGHT ON
RESET TO FACTORY- HOLD THE BLOWER ARROW UP AND THE BLOWER ARROW DOWN
AT THE SAME TIME UNTIL THE UNIT TURNS OFF
 
  • Like
Reactions: rjAKAmoses
Depends on which of the 6 versions of the ABC board you have.

Version 13 b also applies to version 12 b & 11 b
THE A AND B BUTTONS WERE NOT ACTIVE. PRESS THE HEAT RANGE DOWN AND
BLOWER RANGE UP AT THE SAME TIME FOR 5 SECONDS TO ACTIVATE
PRESS THE A BUTTON AND THE HEATRANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE AUGER SETTING. FACTORY SETTING IS 4. THIS CONTROLS
THE AUGER SPEED
PRESS THE B BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE COMBUSTION AIR SETTING. FACTORY SETTING IS 3. THIS
CONTROLS THE COMBUSTION AIR.
RESET TO FACTORY-HOLD IN B & C UNTIL P1 APPEARS. USE THE HEAT RANGE ARROW
INCREASE TO P9 AND PRESS THE ON BUTTON- THE UNIT WILL TURN OFF THE BOARD
WILL BE RESET.

VERSION 32B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THIS VERSION WAS FAMOUS FOR BLOWING FUSES IT CAN ALSO CAUSE THE EXHAUST
AND ROOM BLOWER TO TURN ON AND OFF.
PLEASE TELL THE CUSTOMER WE NEED TO UPDATER THE CONTROL BOARD AND SEND
OUT THE LATEST VERSION TO THEM

VERSION 33 B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THE A AND B BUTTONS SHOULD BE ACTIVE IF NOT PRESS THE HEAT RANGE DOWN AND
BLOWER UP.
THE HEAT RANGE DOWN AND BLOWER SIDE WILL READ THE
AUGER SETTING FACTORY SETTING IS 4 THIS CONTROLS THE AUGER SPEED
PRESS THE A BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE AUGER SETTING FACTORY SETTING IS 4. THIS CONTROLS
THE AUGER SPEED.
PRESS THE B BUTTON AND THE HEAT RANGE NUMBER SHOULD DISAPPEAR. THE
BLOWER SIDE WILL READ THE COMBUSTION AIR SETTING. FACTORY SETTING IS 3. THIS
CONTROLS THE COMBUSTION AIR
RESET TO FACTORY- HOLD IN B & C UNTIL P1 APPEARS. USE THE HEAT RANGE ARROW
INCREASE TO P9 AND PRESS THE ON BUTTON- THE UNIT WILL TURN OFF. THE BOARD
WILL BE RESET

VERSION 34 B
A-AUGER
B-BLOWER
C-AUGER DELAY DURING START UP
C-AUX WILL TURN AGITATOR
THE A AND B BUTTONS WERE NOT ACTIVE. PRESS THE HEAT RANGE DOWN AND
BLOWER RANGE UP AT THE SAME TIME FOR 5 SECONDS TO ACTIVATE. THE A AND B
BUTTONS WILL NOT LIGHT UP WHEN PRESSED
FEED-PRESS THE A BUTTON THE HEAT RANGE NUMER AND BLOWER SPEED NUMBER
SHOULD CHANGE THIS IS THE POUNDS PER HOUR THE AUGER WILL FEED. THE FACTORY
SETTING IS 1.5 THIS IS THE LOW FUEL RATE FOR SETTING NUMBER ONE. DO NOT TELL
THE CUSTOMER THIS IS REFERING TO POUNDS PLEASE REFER TO THIS NUMBER AS
FIFTEEN
FEED-IF YOU PRESS THE A BUTTON TWICE YOU WILL SEE THE HIGH END AUGER SPEED
THE FACTORY SETTING IS 5.0 THIS IS THE AUGER SPEED FOR THE NUMBER 9 SETTING
TO INCREASE OR DECREASE THESE SETTINGS USE THE ROOM BLOWER ARROW UP AND
DOWN
AIR-PRESS THE B BUTTON AND YOU WILL SEE A NUMBER ON THE HEAT RANGE SIDE
AND BLOWER SIDE. THIS IS THE LOW END COMBUSTION BLOWER SPEED (SETTING #1)
THE FACTORY SETTING IS 90
AIR-PRESS THE B BUTTON TWICE AND YOU WILL SEE A NUMBER ON THE HEAT RANGE
SIDE AND BLOWER SIDE. THIS IS THE HIGH END COMBUSTION BLOWER SPEED (SETTING
#9). THE FACTORY SETTING IS 08 WITH C BUTTON LIGHT ON
RESET TO FACTORY- HOLD THE BLOWER ARROW UP AND THE BLOWER ARROW DOWN
AT THE SAME TIME UNTIL THE UNIT TURNS OFF
I can't thank you enough for this information ARC. I appreciate every bit of this information. Also, I wasn't aware there were so many versions of this ABC board. I will check this afternoon when I get home from work for the version I have. Also, my dad has a 6041 with the 4 button board, would it be worth my while to upgrade from the ABC to the 4-button? Thanks again.

P.S. I had a feeling that the numbers for the A button were referencing PPH high and low, same with the B button referencing the combustion fan.