Austroflamm Integra

Mtnman1 Posted By Mtnman1, Dec 30, 2012 at 6:16 PM

  1. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    Hello,
    I hope you all can help, I have a Austroflamm Integra pellet stove, this is the second
    season of using it. the blower motor has a mind of its own and fluctuates up and down, and
    sometimes runs flawlessly. I was emailing someone about it I found on eBay. He says my
    air sensor is bad, but told me to pull it out and look at it, if its covered in soot clean it and
    check for a dark spot on the board. he also recommended resealing the glass and door. I
    brushed off all the soot, and yes there is a dark spot on it. put back in and worked flawlessly
    for about 3 weeks...started acting up again, yesterday I resealed the door, pulled the switch
    again and this time sprayed it with a good circuit board cleaner. cleaned the entire stove,
    blower motor,convection tubes, 8 holes behind the tubes,tube behind the convection tubes
    Etc. put back together, started up......blower fan will not pick up right away goes up and
    down, and now it has a tall lazy flame and smokes real bad....I noticed the door did not have
    the rope gasket at the bottom of the center glass.....I put one there??...Is this still my air
    sensor giving me grief??....it did not smoke before I changed the door and glass
    seals...however I could tell from the pattern on glass after stove ran for a day that it was leaking before I changed the ropes.
    Thanks for your help
    Mtnman1
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  2. Mark_ms

    Mark_ms
    Feeling the Heat 2.
    NULL
    

    Jan 28, 2008
    339
    44
    Loc:
    Upstate NY on VT Border
    When you say "blower motor" are you talking about the combustion motor which should start right upon turning your unit on or do you mean the convection blower that starts up after about 10-12 minutes after start up once your Integra comes up to temperature.
    When you cleaned your unit did you also clean the flue?? A blocked flue will cause a lazy flame and soot as you have improper air flow.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Mtnman1 likes this.
  3. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    Ya the combustion motor, and no that's the only thing I didn't clean and I thought about it and said to my self....self you just did that in November 2012, (we had a good warm fall so I got a late start on going full bore with the stove...lol) and I did it in Oct. of 2011 and did not do it till this Nov. and it was dirty but not blocked, but that don't mean anything, it could be, I buy Pellets from a local lumber mill that makes them them selves, they seem to be a high ash pellet. but only cost me $175.00 a ton...;)...and I notice that they differ from ton to ton....Lol

    Red-E-Fuel pellets
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    The funny thing is it did not do this till after I resealed the door and glass?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  5. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    According to the sticker its a 92,93,or 94....it is not checked....it was a free stove...;)
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. Mark_ms

    Mark_ms
    Feeling the Heat 2.
    NULL
    

    Jan 28, 2008
    339
    44
    Loc:
    Upstate NY on VT Border
    Did you put gasket material at the top of glass?? If you did that may be your problem...and it should be flat 1/4 inch not rope gasket.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    I did, and yes it is 1/4 in flat with a sticky backing you pull off the paper to stick it. now you say that it might have been the top that did not have gasket on it, I kept getting called in the middle of doing this job and was getting a bit distracted, My Wife just had a Hysterectomy...Lol
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    Great news, I replaced the air sensor and fixed the door glass seals, problem solved. no more smoke, no more lazy flame, no more up and down with the speed of the combustion & Convection motors..... getting total burn in the pot, still seems to feed to many pellets tho, I think it could do just as good if the auger feed was shorter.....all good come spring I will send both boards to the guy in California to have them checked out.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    Well my Austroflamm has went down again, now my red light flashes and the auger turns real slow..or pulsates so to speak. can anyone help with that? is it looking like my eprom or board?
    Thanks in advance....
    Cold in Idaho
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  10. Flammam

    Flammam
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2007
    357
    35
    Loc:
    Western, Ma.
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Mtnman1 likes this.
  11. Hdhogger

    Hdhogger
    Feeling the Heat 2.
    NULL
    

    Oct 16, 2012
    258
    47
    Loc:
    Massachusetts
    Here's what I found with my Ausroflamm. When cleaning remove the lower and upper panels in the fire box. Vacuum the ceiling of said firebox along with all areas that require cleaning. After I did this, no more lazy flame. Ash will build up in this area and restrict the combustion blower air flow.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  12. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    I
    cleaned it first off and I had a spare motor and put it on. didnt change the problem
    cleaned it first off and I had a spare motor and put it on. didnt change the problem
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  13. Mtnman1

    Mtnman1
    New Member 2.
    NULL
    

    Dec 30, 2012
    18
    0
    Loc:
    Idaho
    I do that 2 time a week, normal cleaning procedure.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  14. Hdhogger

    Hdhogger
    Feeling the Heat 2.
    NULL
    

    Oct 16, 2012
    258
    47
    Loc:
    Massachusetts
    The only thing I don't see mentioned here is your vent system. Can you describe, and has the system been thouroughly cleanened recently?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  15. Hdhogger

    Hdhogger
    Feeling the Heat 2.
    NULL
    

    Oct 16, 2012
    258
    47
    Loc:
    Massachusetts
    Also, my air sensor is in the air intake tube, so I don't know how this could be covered with soot::P
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  16. Mark_ms

    Mark_ms
    Feeling the Heat 2.
    NULL
    

    Jan 28, 2008
    339
    44
    Loc:
    Upstate NY on VT Border
    If you are sure your auger motor is not the issue you then need to check your high limit switch
    1) Disconnect your stove from outlet
    2) Disconnect wires from high limit switch located on combustion fan and join them together.
    3) plug stove back in, turn on switch on control panel
    4) Both combustion AND convection fans will start. pellets should feed

    Some high limit switches can be reset by pressing on the center of switch.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  17. Flammam

    Flammam
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2007
    357
    35
    Loc:
    Western, Ma.
    The high limit switch is located on the convection blower not the combustion blower. the pof/low limit switch is on the combustion blower
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  18. Mark_ms

    Mark_ms
    Feeling the Heat 2.
    NULL
    

    Jan 28, 2008
    339
    44
    Loc:
    Upstate NY on VT Border
    Oops! all those motors that begin with a "C" confuse me sometimes.....:rolleyes: but yes you are correct!
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  19. skibumm100

    skibumm100
    Feeling the Heat 2.
    NULL
    

    Sep 26, 2007
    278
    37
    Loc:
    Southwest Michigan, formerly Southern NH
    Once you get your stove going again, you might want to adjust your trim pots on the main board. Mine are currently adjusted with the auger feed trimmed all the way down and my air trim turned all the way up. I could still use a little more air, especially at low fire.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...