First, measured performance, then the question.
My Tarm heats 1000 gal pressurized storage through a 5 x 12 x 30 plate hx, 1" ports. The boiler loop is very short, Taco 009, assumed 8 gpm flow.
The tank loop is about 60 feet, 3/4" line, Grundfos UPS 15-58F, 3 speed, with check valve. I have a high temp water filter, 50 micron, on the supply side to the hx.
I just installed a variable area flow meter, which measures 2 - 20 gpm, on the supply side to the hx. Measured flow rates with the Grundfos: Low - 4 gpm, Med - 5 gpm, Hi - 5.5 gpm. Since btu varies with delta T, at an assumed delta T of 30F, btu transfer through the hx is: Low - 60,000 btu/hr, Med - 75,000 btu/hr, Hi - 82,500 btu/hr.
Question: the flow chart for the Grundfos shows on Low 4 gpm = 6' head, which also means that on Med flow should be 9 gpm and on Hi flow should be 12 gpm. Why are the measured flows on Med and Hi so much less than the flow chart indicates? Is it simply related to the flow resistance in a 3/4" line? Will a higher head capacity circulator (Taco 0011 or 0013, for example) materially improve flow performance? To increase flow will moving to a 1" or larger line materially improve flow performance? Is the water filter likely to be the limiting factor on flow?
I do have the ability to temporarily remove the water filter, so I probably can answer the last question myself, but other input will be helpful. Thanks.
My Tarm heats 1000 gal pressurized storage through a 5 x 12 x 30 plate hx, 1" ports. The boiler loop is very short, Taco 009, assumed 8 gpm flow.
The tank loop is about 60 feet, 3/4" line, Grundfos UPS 15-58F, 3 speed, with check valve. I have a high temp water filter, 50 micron, on the supply side to the hx.
I just installed a variable area flow meter, which measures 2 - 20 gpm, on the supply side to the hx. Measured flow rates with the Grundfos: Low - 4 gpm, Med - 5 gpm, Hi - 5.5 gpm. Since btu varies with delta T, at an assumed delta T of 30F, btu transfer through the hx is: Low - 60,000 btu/hr, Med - 75,000 btu/hr, Hi - 82,500 btu/hr.
Question: the flow chart for the Grundfos shows on Low 4 gpm = 6' head, which also means that on Med flow should be 9 gpm and on Hi flow should be 12 gpm. Why are the measured flows on Med and Hi so much less than the flow chart indicates? Is it simply related to the flow resistance in a 3/4" line? Will a higher head capacity circulator (Taco 0011 or 0013, for example) materially improve flow performance? To increase flow will moving to a 1" or larger line materially improve flow performance? Is the water filter likely to be the limiting factor on flow?
I do have the ability to temporarily remove the water filter, so I probably can answer the last question myself, but other input will be helpful. Thanks.