I'm having a new boiler furnace installed in my house (Domusa Dual Therm 35KW). It can use both pellets and logs. I plan to use both. Installer says not to use a Thermal Storage or Buffer Tank. He says the size we'd need won't fit thru the door of the house into the furnace room.
I read this old thread:
And...I'm a bit confused. Okay many people say thermal storage isn't needed with a wood pellet boiler but IS needed with a log boiler due to safety/overheating issues if the power goes out with a load of logs burning. For sure my current boiler has overheated if the primary pump is unplugged so that's a known issue, blows the relief valve.
We will use this boiler to heat our domestic hot water. So that tank is supposed to be 300 liters. Calculations I saw say a 35KW system should have at least 700 liters of buffer for overheating protection (70 gallons per 10,000 BTU heating power or so). So some people say that the domestic hot water tank can be used as a sort of thermal storage. Should I buy a much larger domestic hot water tank then? Currently we have 150 liters which is not enough for our family so 300 liters seems like enough but I'm willing to go bigger if needed.
House is not zoned, does not have any temperature gauges in the rooms to communicate with the boiler. It's all quite old school. So there won't be any "calls" made to the boiler, just from the control panel and domestic hot water tank.
As far as Domusa goes they say any of the 5 following installation methods are acceptable:
17.6 Managing BT and BT-DUO buffer tanks
Parameter P.08 is used to set the type of hydraulic installation that has been used for the BT or BT-DUO buffer tank. This parameter depends on the instllation and must e set by the installer once the buffer tank has been assembled. The factory default value is 0, management function of BT buffer tanks is disabled. The elctronic control of the DualTherm boiler is able to manage the operation of 4 different types of installation.
Function Disabled
Installation with Sanit DHW tank after BT tank and control by temperature sensor
Installation with Sanit DHS tank before BT tank and control by temperature sensor
installation with Sanit DHW tank after BT tank and control by thermostat
Installation with Sanit DHW tank before BT tank and control by thermostat
Ultimately I just want a better heating system for my house and family. I don't really trust my installer (part time sub-contractor to the company I bought from) and I'm looking for other opinions before we go ahead with the install.
I read this old thread:
Does a Pellet Boiler Need Storage?
I'm thinking it wouldn't, but could someone verify? Also nothing special for a chimney - right out the side of the house. Might save install cost anyway.
www.hearth.com
And...I'm a bit confused. Okay many people say thermal storage isn't needed with a wood pellet boiler but IS needed with a log boiler due to safety/overheating issues if the power goes out with a load of logs burning. For sure my current boiler has overheated if the primary pump is unplugged so that's a known issue, blows the relief valve.
We will use this boiler to heat our domestic hot water. So that tank is supposed to be 300 liters. Calculations I saw say a 35KW system should have at least 700 liters of buffer for overheating protection (70 gallons per 10,000 BTU heating power or so). So some people say that the domestic hot water tank can be used as a sort of thermal storage. Should I buy a much larger domestic hot water tank then? Currently we have 150 liters which is not enough for our family so 300 liters seems like enough but I'm willing to go bigger if needed.
House is not zoned, does not have any temperature gauges in the rooms to communicate with the boiler. It's all quite old school. So there won't be any "calls" made to the boiler, just from the control panel and domestic hot water tank.
As far as Domusa goes they say any of the 5 following installation methods are acceptable:
17.6 Managing BT and BT-DUO buffer tanks
Parameter P.08 is used to set the type of hydraulic installation that has been used for the BT or BT-DUO buffer tank. This parameter depends on the instllation and must e set by the installer once the buffer tank has been assembled. The factory default value is 0, management function of BT buffer tanks is disabled. The elctronic control of the DualTherm boiler is able to manage the operation of 4 different types of installation.
Function Disabled
Installation with Sanit DHW tank after BT tank and control by temperature sensor
Installation with Sanit DHS tank before BT tank and control by temperature sensor
installation with Sanit DHW tank after BT tank and control by thermostat
Installation with Sanit DHW tank before BT tank and control by thermostat
Ultimately I just want a better heating system for my house and family. I don't really trust my installer (part time sub-contractor to the company I bought from) and I'm looking for other opinions before we go ahead with the install.