Does it matter if a circ pump is pulling from a tank or pushing to a tank. Plumbing in my circ. pump from primary tank to storage tank.
Thanx. Huff.
Thanx. Huff.
Hunderliggur said:Assuming you have a closed system, no there is not significant difference. What is a primary tank in relation to a storage tank?
I used to be a Bruins fan before 1970 ,my dad was a bruins fan too. Than we had to jump ship when we got our own team here.NovaScotian said:Huff, nice looking setup, but I think your boiler would work better if it had a "B" on the loading door. Ha Ha
Go "B"s Go.
Paul
in hot water said:Nice! It common to see the circ pumping into the boiler with restrictive heat exchangers type boilers, like many of the mod con types. This way the boiler HX sees the pressure increase the pump provides and helps keep them from flashing.
In your case with "wide open" boiler passageways it would not matter. Cooler is always better for a motor, so on the return you would be in a cooler flow, the pumps are typically rated to 225F operating max.
Add a float type air vent on top of your buffer tank, in that ball valve. That is a great place to slow the flow and capture air in that domed up section.
Calculate the entire water volume to size an expansion tank, that one looks a tad small?.
hr
goosegunner said:Lets see some better pictures of your vent hood.
gg
huffdawg said:goosegunner said:Lets see some better pictures of your vent hood.
gg
Here u go GG
Its not piped in yet
I can see how hot water gets from boiler to primary tank, but how does hot water get from boiler (or primary tank) to storage? How does hot water get from storage to primary tank? Are you going to use two pumps from primary tank to storage, one going one way and one going the other? How would you control that?huffdawg said:Here's some pic's of the primary tank.
DaveBP said:Is your primary tank intentionally set up as a hydraulic separator by design?
ewdudley said:I can see how hot water gets from boiler to primary tank, but how does hot water get from boiler (or primary tank) to storage? How does hot water get from storage to primary tank? Are you going to use two pumps from primary tank to storage, one going one way and one going the other? How would you control that?huffdawg said:Here's some pic's of the primary tank.
huffdawg said:ewdudley said:I can see how hot water gets from boiler to primary tank, but how does hot water get from boiler (or primary tank) to storage? How does hot water get from storage to primary tank? Are you going to use two pumps from primary tank to storage, one going one way and one going the other? How would you control that?huffdawg said:Here's some pic's of the primary tank.
I'm not sure yet Eliot . Do you or anyone else have any ideas.
Thanx Huff
Don L said:huffdawg said:ewdudley said:I can see how hot water gets from boiler to primary tank, but how does hot water get from boiler (or primary tank) to storage? How does hot water get from storage to primary tank? Are you going to use two pumps from primary tank to storage, one going one way and one going the other? How would you control that?huffdawg said:Here's some pic's of the primary tank.
I'm not sure yet Eliot . Do you or anyone else have any ideas.
Thanx Huff
Do you have a diagram of your plan?
Do you think it would work to pipe the boiler directly to storage, and then have a loop that runs from storage to the primary tank? Then the boiler always knows what to do and so does the pump from storage to primary.huffdawg said:Heres a rough sketch Don . There are 1-1/4" ports plumbed into the primary tank for the storage already.
goosegunner said:huffdawg said:goosegunner said:Lets see some better pictures of your vent hood.
gg
Here u go GG
Its not piped in yet
Very nice! I could use something like that in My shed. What are your plans for ducting and fan?
gg
ewdudley said:Do you think it would work to pipe the boiler directly to storage, and then have a loop that runs from storage to the primary tank? Then the boiler always knows what to do and so does the pump from storage to primary.huffdawg said:Heres a rough sketch Don . There are 1-1/4" ports plumbed into the primary tank for the storage already.
ewdudley said:Do you think it would work to pipe the boiler directly to storage, and then have a loop that runs from storage to the primary tank? Then the boiler always knows what to do and so does the pump from storage to primary.huffdawg said:Heres a rough sketch Don . There are 1-1/4" ports plumbed into the primary tank for the storage already.
in hot water said:Flow reversal can be done a couple ways. On mine I have two pumps facing each other. But remember the internal checks need to be removedI'm not that pleased with the operation it tends to thermosiphon when the checks are left out.
I will try a 4 way valve with a motor that drives it from one extreme to the other. I had a sample of this valve a few years back to correct a radiant job that had a 1000' loop installed! The valve would flow into the loop from one end for 30 minutes, then flow from them other for 30 minutes. It actually did help the floor temperature even out by flip flopping the flow.
The valve was built up by Leif at Paxton. Basically it had a Honeywell 24V actuator motor bolted on. I think Bellimo also offers this actuator.
So when the boiler tank is hot a ∆ T control starts the pump with valve allowing flow as in the top drawing. When the storage is within 5 degrees of the boiler tank the pump stops. A second ∆ T function would start them pump, flop the valve and take that energy out of the storage and back to the boiler tank.
At least that is how I imagine this control logic to work. I'm open for suggestions.
The heat loads all pull from that boiler/ separator tank.