Maverick,
I read a lot about suggested heat loss calcs on this forum, which makes total sense on new construction and complete house remodels.
When you are just replacing a boiler, the real issue is what radiation you have installed in the house. The Heat Loss calc's are used to size the amount of radiation required to heat a given space, but I'm not sure that calculation makes much sense on a boiler replacement. If your existing House Radiation (BaseBoard and DHW) is staying the same, I would add up your existing radiation and then calculate the Max BTU's needed to support that radiation loading.
In my case, I have about 2000sqft, living in VT where below-0 is very common. I have 2 Heating zones (60ft and 40ft of BaseBoard) and my Indirect DHW Tank, which get's priority over the heating zones. So my Max Boiler loading is 100ft of BB at approx 600BTU/ft=60,000BTU Max Boiler load. The DHW could consume another 30,000-50,000 BTU's, so without priority control I would need (60K + 50K = 110KBTU's) to handle my max heating load. With the priority control on my DHW tank, and 100ft of BaseBoard, the most my house could ever consume from ANY boiler is 60,000 BTU's (regardless of the house insullation or temperature outside)
Buying a larger boiler without water storage, will only cause short-cycles on the boiler and lower your overall efficency ! So, I purchased an 80K-BTU boiler (larger for future expansion), and then down fired the Boiler with a 0.5gph nozzel = 60K BTU's. The 60K BTUs heat my 2,000sqft house better than my old 110KBTU Boiler with the DHW Coil, and my energy costs have gone way down.
Also, when you calc BTU's of needed Heat, you need to consider the boiler efficency. Real BTU's of Heat = 139,000 BTU's/gal x 0.85 boiler efficency = 118,000 BTUs of usable heat energy.
In summary, Heat Loss Calc's are not as important for boiler replacements, when the radiation stay's the unchanged. If your existing house radiation services your home heat loss OK, then just calculate the Max BTU Load your boiler will ever need to service at one time,using your existing radiation that is installed (using 580-610 BTU\ft for Base Board). Make sure you include any DHW loading too, if DHW is required when all heating zones are in use.
Just my humble opinion, which has worked well for me at my house (110K BTU boiler was replaced with a 60K BTU Boiler).
VT_Bubba