Might not be the right forum for this as it does involve a wood stove, but its not the main focus.
So earlier this week I got a new 2stage furnace and heat pump installed. This install included a HZ432 Honeywell zone controller for the newly seperate zones for the top and bottom floor. Each floor has a ecobee3 lite that can only call for heat, cool or fan, and the zone controller decides how many stages of heating or cooling to use depending on if one or both floors are calling. Additionally it also handles the automatic switch from using the heatpump vs using the furnace.
Right now its set to do that swap at 32f, and the installer instructed me to change that if it seemed like the heatpump could or couldn't keep up at that temp.
The heatpump beats out propane in cost/btu across its entire operating range if the spec sheet is to be believed, so if it can keep up with the homes heating demands I would obviously always want to use the heatpump.
Issue that occurs to me though is I still have a wood stove that I intend to heat primarily with. If I got the wood stove + heatpump going they should have absolutely no problems covering my homes heating requirements with the stove serving as the bulk heat source and the heatpump adding a bit on top while helping to circulate the heat. However if we are away during a particularly cold time I doubt the heatpump could keep up on its own. I thought these two operating situations were simply at odds and I'd have to settle with just setting that crossover temp at whatever I felt the heatpump could handle alone, even if its more costly.
However while looking over the manual for the HZ432 I did notice two settings that look like they might be of value.
Dual Fuel Changeover; which has the following two options
Allow panel to changeover from heat pump to
fossil fuel based on outdoor temperature, or
allow second stage call to changeover panel
to fossil fuel for a minimum of one hour when
outdoor temperature is above OT balance tem-
perature setting. Multistage changeover is only
available on dual fuel applications configured
for 2 heat pump stages.
and then this setting
Dual Fuel Mstage Changeover Time; which can be set to anything between 15 and 180 minutes
Description: Sets fossil fuel changeover delay time.
Notes: Sets number of minutes to delay fossil fuel when calling for second stage heat.
Now at first glance it looks like one of these may solve my problem. So far it seems the 1st floor is the primary one calling for heat, with the 2nd floor only calling for it occasionally for a few minutes at a time. If the heatpump was falling behind I'd assume both floors would end up constantly calling for heat, and it almost seems like one of these two settings would let the system detect that situation and changeover to the furnace automatically after either an hour, or some time between 15-180 minutes. Not sure if we got anyone who might have experience here with something like this, cause I might just be misunderstanding it and these mean something else entirely than what I'm thinking.
So earlier this week I got a new 2stage furnace and heat pump installed. This install included a HZ432 Honeywell zone controller for the newly seperate zones for the top and bottom floor. Each floor has a ecobee3 lite that can only call for heat, cool or fan, and the zone controller decides how many stages of heating or cooling to use depending on if one or both floors are calling. Additionally it also handles the automatic switch from using the heatpump vs using the furnace.
Right now its set to do that swap at 32f, and the installer instructed me to change that if it seemed like the heatpump could or couldn't keep up at that temp.
The heatpump beats out propane in cost/btu across its entire operating range if the spec sheet is to be believed, so if it can keep up with the homes heating demands I would obviously always want to use the heatpump.
Issue that occurs to me though is I still have a wood stove that I intend to heat primarily with. If I got the wood stove + heatpump going they should have absolutely no problems covering my homes heating requirements with the stove serving as the bulk heat source and the heatpump adding a bit on top while helping to circulate the heat. However if we are away during a particularly cold time I doubt the heatpump could keep up on its own. I thought these two operating situations were simply at odds and I'd have to settle with just setting that crossover temp at whatever I felt the heatpump could handle alone, even if its more costly.
However while looking over the manual for the HZ432 I did notice two settings that look like they might be of value.
Dual Fuel Changeover; which has the following two options
- Dual Fuel Changeover by OT Temp (outdoor temp)
- Dual Fuel Changeover by OT Temp + multistage call
Allow panel to changeover from heat pump to
fossil fuel based on outdoor temperature, or
allow second stage call to changeover panel
to fossil fuel for a minimum of one hour when
outdoor temperature is above OT balance tem-
perature setting. Multistage changeover is only
available on dual fuel applications configured
for 2 heat pump stages.
and then this setting
Dual Fuel Mstage Changeover Time; which can be set to anything between 15 and 180 minutes
Description: Sets fossil fuel changeover delay time.
Notes: Sets number of minutes to delay fossil fuel when calling for second stage heat.
Now at first glance it looks like one of these may solve my problem. So far it seems the 1st floor is the primary one calling for heat, with the 2nd floor only calling for it occasionally for a few minutes at a time. If the heatpump was falling behind I'd assume both floors would end up constantly calling for heat, and it almost seems like one of these two settings would let the system detect that situation and changeover to the furnace automatically after either an hour, or some time between 15-180 minutes. Not sure if we got anyone who might have experience here with something like this, cause I might just be misunderstanding it and these mean something else entirely than what I'm thinking.