Howdy folks,
I am troubleshooting an auger timeout error code with the Fahrenheit Endurance 50 furnace.
Here's a run down of what's been confirmed / tried:
Could the blower/limit switch still be the problem, even though I got the error with the hi-limit bypassed? Maybe I should be investigating the auger more since it didn't take to the prime button briefly this morning?
Appreciate any guidance.
I am troubleshooting an auger timeout error code with the Fahrenheit Endurance 50 furnace.
Here's a run down of what's been confirmed / tried:
- Error will appear seemingly at random, sometimes at start-up even.
- The auger seems to operate fine, as viewed with rear cover removed
- Blower operates
- Hopper was cleaned to ensure no jam
- Hi-limit switch was bypassed and error still occurred
- The assumed culprit due to above was the control board (even emailed with folks at Fahrenheit to confirm).
- Installed new (expensive) control board today. Error immediately shows up.
- I DID notice that when I tried to 'prime' the auger, it didn't want to spin for a bit. But then later in the startup process it started operating fine. FWIW, the startup process is really slow with lots of vacuum pumping (but no vacuum error codes).
- I was able to run the machine on manual mode for a bit with no error, but I HAVE previously gotten the error on manual mode.
- When I tried to operate on thermostat mode (our typical configuration) it errored pretty quickly (the thermo might not have been calling for heat). It has worked before with the thermostat.
Could the blower/limit switch still be the problem, even though I got the error with the hi-limit bypassed? Maybe I should be investigating the auger more since it didn't take to the prime button briefly this morning?
Appreciate any guidance.