My buddy is installing a 1000 gallon tank and his total volume for system is 1200 gallons. What would you recommend for expansion volume?
My buddy is installing a 1000 gallon tank and his total volume for system is 1200 gallons. What would you recommend for expansion volume?
Two extrol 110s will do it. I have one 160 and it works also but it is border line.
Been checking into this stuff some.
The 90v is 44 gallons with 34 acceptance.
The 110v is 62 gallons with 34 acceptance.
I thought acceptance was key - so no advantage going with the 110 over the 90?
(Only difference is the 110 is a foot higher, on the face of it).
Just a bit confused that's all...
Expansion tanks can go pretty much anywhere, but often it is important to connect to the system at a particular point, in which case you have to run a line all the way from the tank(s) to that point. The distance could be a couple hundred feet if you're using 3/8" or 1/2" PEX (for instance) to tie it in.I seem to be spending a lot of thinking time on my expansion situation and how to improve it without intruding into places where I really don't want to or can't put it.
sx110v seem to cost almost $500 only about 20 bucks less than a sx160v. I'm looking at a sx160v and a sx40v which would cost about $640 instead of a thousand bucks for 2 sx110v's. Am I missing something or wouldn't the cheaper option yield a combined 106 gal with 54 gal acceptance?Two extrol 110s will do it. I have one 160 and it works also but it is border line.
Expansion tanks can go pretty much anywhere, but often it is important to connect to the system at a particular point, in which case you have to run a line all the way from the tank(s) to that point. The distance could be a couple hundred feet if you're using 3/8" or 1/2" PEX (for instance) to tie it in.
But also, if you mount the tank below the connection point to the system, several feet for example, you do add some static pressure to the tank and slightly reduce the expansion capability. Unless the tank is sized dead nuts on, this should not be an issue.
But isn't the inverse also true: If the expansion tank is mounted above the boiler/circulator it can ADD usable expansion volume?
Like ,say, up on the second floor in a basement boiler system>
But isn't the inverse also true: If the expansion tank is mounted above the boiler/circulator it can ADD usable expansion volume?
Like ,say, up on the second floor in a basement boiler system>
Yes. In my case, the expansion tank connects to the system just upstream of the boiler circulator.Sure, but you do want the pump located as close as possible to the tank connection. Locating the tank upstairs, you would want to pipe it down to the circ location