FNUG,

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

boB48

New Member
Jan 7, 2015
7
Otsego - Plainwell Mi.
OK, My homemade boiler ...
Was working pretty good last week but not now, not so good now.draft fan kicks on at 160 and off at 180 water reads about 120 @ the coil and lower at 110 . circ pump runs constantly inside the basement ,and side arm worked awesome last week.It would peal skin in the shower . i know it's way cold .I just keep putting the wood to it . any suggestions would b really appreciated. Cold in plainwell.
 
May be undersized. An undersized boiler can perform just fine in moderate temps, but fail to keep up when it gets a lot colder. If it's not too small for the space you're heating, you may have some heat exchange issue, such as a flat plate heat exchanger the wrong size or set up wrong.

Hard to say what your problem is without any details and probably difficult to diagnose even with more detail. Could be a wide range of things, including a combination of factors.

Since it's warming back up over the next week, see if it starts performing well again. If so, that's a big clue.
 
Given that actual boiler output is completely unknown about all you can do is check the basics.

Determine actual water temp in the boiler by checking with another thermometer or gauge.
Make sure circulation is good.
Check temp differential between supply and return. Should be less than 20* under normal circumstances and flow rates.

Other than that, as Eric said if it catches up next week in when it's in the 20's it's pretty obvious that it doesn't produce enough heat to keep up when its cold.
 
I have no idea what the title of this thread means.

But anyway, am I reading your post right that you have 160-180 water leaving your boiler, but it's only 120 when it gets to your coil? If so there is something desperately wrong there. What do you have for underground piping?
 
I had PM'd Bob some yesterday, figured I would post it here for everyone to ruminate on.

He has a water temp of 163 at the boiler, but the outlet fitting at the boiler is only 136. So it sounds like either a water flow issue or some thermometer wonky-ness. He bumped up the aquastat 10 degrees to see if the boiler temps can get higher. Might have to move where the aquastat reads to get good hot water to circulate to the house.

Bob, if you check this thread, did the aquastat change help things at all?
 
Is this like an OWB? If so where are you taking the water from? If you have it so the supply is pulling from near the return you will get this type of issue. That's why OWB's take water from lower in the tank, and return it higher and tube it to the front. My brother misunderstood which pipe to use and was trying to take water from the top ports. Which in theory should get the "Hottest" water. But it was causing a lock in the tank and he was just pulling the expended water back into the supply again. Swapped them around and everything worked as it should.
 
Status
Not open for further replies.