Did you try a manual reset?
Also is DIP switch 5 set correctly?
Dip switch 5 is for ESP type
This switch needs to be off for any ESP probe other than RED.
Therefore, for the Black Probe, DIP switch 5 should be off.
Here is the complete list of status blinks 1-6
No one manual has them all.
Harman Status Light Blinks (Error Codes)
2 Blinks only for P61-2 updated manual stove
5 Blinks only for Auto Light Stoves
1 Blink: Indicates control board self diagnostic failure.
This requires a manual reset*.
2 Blinks:Indicates that the jumper (J2) on the rear
of the control board is not connected. Without this
jumper the unit will only burn at minimum rate.
3 Blinks: Indicates ESP (Exhaust Sensing Probe)
failure. This requires a manual reset*.
4 Blinks: Can occur only in Room Temp Mode and
indicates Room Sensing Probe failed or not installed.
If a Room Sensing Probe is then installed the status
light will automatically reset.
5 Blinks (In Igniter Auto. Mode Only): Indicates
that the unit has failed to light within the 36 minute
start cycle. To reset - Turn Mode Selector to "OFF",
then turn to either mode again.)
6 Blinks : Indicates that the control has calculated poor
or incomplete combustion occurring for more than 50
minutes. See Troubleshooting section for more details.
* Manual reset, disconnect power cord for a few
seconds and reconnect. If error still occurs call your
Dealer.