When I decided to build a garage last year, I knew I needed to have radiant floor heat. Before that, I was heating the house with a Breckwell Big E that I had added a coil, to heat water for an air to water heat exchanger in my air handler. There is a thread somewhere on here of that project. I knew the pellet stove would not generate enough energy to also heat a 900 square foot concrete slab.

In March of this year I purchased and installed a Central Boiler Classic Edge 350. I plumbed it to the house, hot water heater and garage floor with no storage. I only needed to run the stove for about 2 weeks before it was warm enough to not need heat. In that 2 weeks I found very quickly, that I needed storage. The first night I heated the garage, the boiler ran great and burnt the entire load of wood. After the floor was up to temp, I would have a couple nights that the fire went out due to little to no heat load.

Against a good bit of what I read on this forum, I used home heating oil tanks for my storage. The system is open, and I used brand new tanks. The main reason for heating oil tanks, was that was all I could get to fit through the door to my basement, that actually had some decent volume, and was affordable after spending so much on the stove.


[Hearth.com] My first wood boiler, storage and data monitoring


In that corner of the basement is the sump pump for the house, so if there is a leak, it should at least drain into the sump. The tanks are on legs about 6 inches off the ground, and have drains plumbed together into a valve that goes into the sump pit.

I used the top 2" npt ports of the tanks for all my connections. I made pipes for my return to the boiler and the returns from my heating loops.
[Hearth.com] My first wood boiler, storage and data monitoring [Hearth.com] My first wood boiler, storage and data monitoring

The pipes for the return to the boiler is about 4" off the bottom of the tanks. The return pipes from my loops are about 12" from the bottom. My logic was that the water returning from the loops would still hold heat. Not sure that mattered at all but, that's how I did it.
[Hearth.com] My first wood boiler, storage and data monitoring


Either end, the 2" pipe, is the line coming from the boiler, and the feed to the pumps. The 2" pipe was a nightmare to get leaks to stop, so I ended up switch it to one inch pipe. The pump on the right is the feed to the house. I had to switch that to the return side, as it kept losing prime somehow.

The first thing I noticed when I turned the pump on from the boiler, it created pressure in the tanks and bulged them. With the pump running, I am seeing about 5 psi. It took me a little while to figure out why, when it should have been obvious. The pump on the boiler is on the hot side, pushing water into the house. Pressure is created in order for the water to push back into the stove. As soon as the pump is turned off, the pressure goes away.

The tanks will be insulated with 2 part urethane 2lb foam. I will build forms around the tanks with plywood, and pour the foam in. There will be about 6" thick foam around the tanks. Here is a picture of small batches I was mixing and pouring under the tanks, to make sure I got good insulation on the bottom.
[Hearth.com] My first wood boiler, storage and data monitoring


I will take the foam up to just near the fittings on top, then find a different way to insulate the tops. I want to be able to make changes, or fix leaks relatively easily.

I know the biggest thing with using these tanks, is going to be water treatment. As of right now, my nitrite levels are perfect, at least according to the test kit that came with the boiler but, my PH is 7. I going to add some sodium hydroxide to try to raise the PH to about 8 to 9.

Data monitoring will be done through a ControlByWed X300. The X300 will control my pumps based on set temperatures from the 8 sensors.

I don't want this to get anymore long winded. I love seeing peoples projects and builds, so I though I would add my own. I'm open to all questions and comments.
 
Forgot a picture of my "control center". I run the stove and pumps off an APC 2200 ups with four AGM batteries. The main reason was to keep the pump for the garage running, and prevent a freezing situation.
[Hearth.com] My first wood boiler, storage and data monitoring
Not sure why the picture rotates when I upload it.

I use the X300 to control what the pumps do during certain conditions. I can set it so that if the tank temperature drops below a set point, it will shut off the pump in the house, to keep from pulling heat back out of the water heater.
I currently have it setup with a probe drilled into the outer edge of my garage floor. If the floor gets below 40 degrees, the pump will kick on, and only circulate water through the outer loop. Once it reaches 70 degrees, the pump will shut back off. The garage thermostat can turn the pump on, and also open the 3 zone valves on my 4 loop manifold. I did not insulate the outer edge of the concrete for the garage. It was mainly oversight on my part when building it. Until the day comes that I have equipment there to dig back down to the footers, this solution, I'm hoping, will keep the water from freezing around the edge.
 
As long as I am waiting on a phone call from Honeywell I have a couple of questions;

You have Hydronic circulators not pumps. there is big difference.

Where is your vent line from the top of the tanks? It does not appear that you have a vent line coming through the roof with a U to vent excess pressure against the roof? You need a vent line.

The open system vent on your boiler is not enough for your plumbing.


YOU need one coming from the top of both tanks to the roof with a large U to allow the water pressure to vent through the roof.
If you have not done it yet add a few drops of Dawn Dish Soap to get rid of the air bubbles.
If you have not insulated the tanks yet hold off on that as the heat shedding is something you need to allow.


Why to do you want anything but a neutral PH????????????????????????????????????????????????????? You need a near neutral
PH with the tanks in the basement being full all the time.


Right now you have both circulators fighting with each and not creating a point of "no pressure change" as they are plumbed and you need to move one of them.

With your plumbing as it is now the water is not mixing and all the hot water is staying at the top of the tanks AND you are creating a huge amount of turbulence that will destroy your circulators.

You need to do much more work before you go any further.

Please in vest in a copy of "Pumping Away" and "Classic Hydronics" written by Dan Holohan and available at Barnes and Noble or
(broken link removed)


if and when you move a circulator you can plumb in a dip tube in the two inch NPT fitting to near the base of the tank to keep the water from stratifying.


You also need a vacuum gauge for each circulator on the suction side of the flange disconnects and pressure gauge on the discharge side of the circulators.


Ideally the vent pipe should be at least 2 inches and plumbed into the top of the tanks to allow a zero pressure difference in both tanks and to eliminate any chance of the tanks rupturing or collapsing from a large pressure gradient.

You also need to keep the garage loop hot all the time as the lag time needed to heat the floor will be huge.


Please do not hate for asking but is it too late to move one tank to allow them to be plumbed in series as your system is fighting itself now as it is plumbed.

if you do that you can have flooded suction for the circulator and it will not be working as hard either.



You may also need several steel expansion tanks mounted in the ceiling joists in the basement to
create a stable 12 pounds of pressure for your system as your circulators are creating at least 18PSI and fighting each other because you have no point of pressure change the way the plumbing is now set up-the reason the tanks started to collapse on you. if you had a 2 inch vent to the roof they would not do that.

Ideally the single circulator or both circulators need to plumbed at the bottom to have flooded suction with a large isolation flange.

With a flooded suction piping system you could use one circulator and split the flow to your two zones provided you vent the tank to the roof line with a U elbow and screen set up to prevent icing up or plugging see below


You need need a rubber vent pipe boot for the pipe through roof. The pipe through the roof must at least a foot in length to be above the roof, one 90 degree elbow, one short nipple nipple, and one more ninety degree elbow.
 
Last edited:
Pardon my vernacular.

The vent line for the tanks is the line running back to the boiler. The boiler is an open system, and the highest point in the system.

Central boiler wants the PH level between 8 and 9. For the purposes of the warranty on the boiler, I want the water conditions exactly where Central boiler wants them to be.

From what I can find about a point of no pressure change, it seems to apply to closed systems. Can you please elaborate a little more on this.

The garage loop will depend on a demand for heat from the thermostat. I wouldn't want to constantly heat the floor, as the temperature would continue to climb.

Nothing about my system is closed, so I'm confused how I would need expansion tanks.
 
Pardon my vernacular.


Nothing about my system is closed, so I'm confused how I would need expansion tanks.

Your water volume will increase by approximately 4% when the water temperature is raised from 33F to 180F. That is a ballpark percentage and will never exceed 5% unless flashing to steam. A volume of 1,000 gallons x .04 = a 40 gallon increase.
 
Pardon my vernacular.

1. The vent line for the tanks is the line running back to the boiler. The boiler is an open system, and the highest point in the system.

2. Central boiler wants the PH level between 8 and 9. For the purposes of the warranty on the boiler, I want the water conditions exactly
where Central boiler wants them to be.

3. From what I can find about a point of no pressure change, it seems to apply to closed systems. Can you please elaborate a little more
on this.

4. The garage loop will depend on a demand for heat from the thermostat. I wouldn't want to constantly heat the floor, as the temperature
would continue to climb.

5. Nothing about my system is closed, so I'm confused how I would need expansion tanks.


====================================================================================================

Hello brack86svo,


"Resistance" to water flow is what creates the pressure in a cool or heated hydronic system. Your circulators are pushing water through the pex and fitting and each and every foot of PEX and every fitting and foot of steel pipe is creating the resistance to flow.


number one: are you saying that the cool water return line to the boiler is the vent line????

number two: be sure to have boiler treatment on hand as your going to need it due to the airspace above the water line.

number three: the point of no pressure change applies to all hydronic systems either open or closed as it relates to the pressurised circulation of water. right now your circulators are fighting against each other and trying to create 12-18 PSI in the current plumbing connection that you have.

number four: your going to want to keep the slab some what warm all the time as it will take forever to heat up and by keeping the slab warm you will reduce the overall demand for heat as the slightly cooler water will be coming back to the boiler and storage.

number five: your water storage is "closed" and feeding water back and forth to the garage, the boiler, and your storage. The only open area is the boiler air space. that is why I said the tanks themselves need to be vented to atmosphere at the highest point in your system.

The water weight in the boiler itself is creating pressure into your basement storage tanks. Oil tanks are only good for one atmosphere in pressure 14.28 pounds psig.


Venting pressure from the top of these two tanks to a roof vent is the only safe way to do this with what you have.

Is it too late to think about putting the tanks in the garage and running a length of thermopex along the ground to the boiler for now and burying it later as heating season is only a few weeks away.
In that way one circulator can be pulling heat away from the boiler to storage and the other one can be used to heat your homes heating loops and the garage.

I am not trying to hinder you my friend, but the basic physics for hydronic heating and thermal expansion are your enemies here and I do not want to see you dealing with a ruptured set of tanks and no heat in your house.
 
Last edited:
====================================================================================================

Hello brack86svo,


number one: are you saying that the cool water return line to the boiler is the vent line????

number two: be sure to have boiler treatment on hand as your going to need it due to the airspace above the water line.

number three: the point of no pressure change applies to all hydronic systems either open or closed as it relates to the pressurised circulation of water. right now your circulators are fighting against each other and trying to create 12-18 PSI in the current plumbing connection that you have.

number four: your going to want to keep the slab some what warm all the time as it will take forever to heat up and by keeping the slab warm you will reduce the overall demand for heat as the slightly cooler water will be coming back to the boiler and storage.

number five: your water storage is "closed" and feeding water back and forth to the garage, the boiler, and your storage. The only open area is the boiler air space. that is why I said the tanks themselves need to be vented to atmosphere at the highest point in your system.

The water weight in the boiler itself is creating pressure into your basement storage tanks.oil tanks are only good for one atmosphere in pressure 14.28 pounds psig.

Yes, the only vent from the tanks is the return line to the boiler, and the boiler is vented.

Right now, the boiler is pushing water into the tanks. The garage loop circulator is on the supply side, and the house circulator is on the return side. If I run just the house and garage circulator, I have no pressure in the tanks. The only time I see pressure is when I run the boiler pump.

So you're saying that I need to have a vent coming from the tanks that reaches higher than the vent on top of the boiler itself, as that is the current highest point?

I have about 700 gallons of water storage between the tanks and boiler, so how would I add open expansion?
 
From page 116 from of Classic "Hydronics" written by Dan Holohan


"While were looking at old tanks, I want to mention what goes into sizing a compression tank.
You have to consider these things:

1. The amount of water in the whole system

2. The difference in pressure between the feed-valve setting and the relief valve setting

3. And the Average water temperature of the system on the coldest day of the year."


===========================================================================


A gravity hot water system has expansion to the atmosphere via a roof vent as I described. The basement tanks are going to act as
the boiler reservoir essentially and the tanks have to vented from the top UNLESS you hang a seventy gallon tank in the ceiling with pipe straps or a series of 7 15-gallon tanks in the ceiling joists cross connected with a common header pipe feeding all seven tanks with an "Airtrol fitting in each tank tapping that allows hot water and air bubbles to rise and cold water to drain back to the tanks. this gives you 70 gallons of expansion

Short of that having a larger vertical steel expansion tank in the attic with a vent pipe through the roof may be your only other option.


Your going to need a plumber that deals with gravity hot water heat or a B+G technical sales representative to come to your home to look at your current system as you may end up moving the two tanks to the garage using them as nurse tanks in series to the new boiler if you have the room in the garage for them.






I am not trying to spend your money I just want to help you.
 
I'm pretty sure oil tanks are not good for 14 psi. I would suggest that even 5 is too much, by a factor of about 2 or so.
 
I'm pretty sure oil tanks are not good for 14 psi. I would suggest that even 5 is too much, by a factor of about 2 or so.

The 14 psi he was referring to is barometric pressure, I'm pretty sure anyway.

If I put an expansion tank higher than the boiler itself, wouldn't it just push the water out the top of the boiler?
 
Maybe. But we know very little about your system arrangement & layout. Where is all the extra water going now that gets made when your system goes from cold to hot?
 
Maybe. But we know very little about your system arrangement & layout. Where is all the extra water going now that gets made when your system goes from cold to hot?

It would go into the boiler. The boiler has a vent pipe on top of it, and is the highest point in the system. From what I have found, every 1.8 degrees in temperature increase will result in an increase of 1.0002 in an open system. So if I have 700 gallons at 40 degrees, and heat it to 185 degrees, I should have about 712 gallons. I would think the storage tank of the wood boiler would be able to take on this expansion. The wood boiler has a 150 gallon storage tank, that is only to be filled to certain level due to expansion.

I'm not doubting the need for venting my storage tanks, I'm just trying to understand the need for expansion if the system is already vented to the atmosphere, and my expansion should only be 12 gallons, and any pressure from expansion would just get pushed out the vent of the boiler.
 
Last edited:
There might be issues, if the expansion from heat pushes out water, then the system cools some & the water level drops. That drop would create an empty space at the top of the boiler which may be larger than what the manufacturer intended (due to the significantly extra volume of water in the system), and create more corrosion potential in that empty space. I am thinking the increased back & forth due to the increased volume would pull more oxygen into the system, also increasing the corrosion potential. If you stay on top of the chemicals, it might help - but I think the empty space at the top would still be prone to corrosion. Have read lots of bad stories about some OWBs corroding out at/around the water line.

We also still don't know much more about other system details - such as elevation difference between the bottom of your tanks & the top of your boiler. But the fact that you bulged your tanks just from having your circ running (I think I read that right) would make me quite apprehensive.

Not sure I'll be able to add much more to this one.
 
There might be issues, if the expansion from heat pushes out water, then the system cools some & the water level drops. That drop would create an empty space at the top of the boiler which may be larger than what the manufacturer intended (due to the significantly extra volume of water in the system), and create more corrosion potential in that empty space. I am thinking the increased back & forth due to the increased volume would pull more oxygen into the system, also increasing the corrosion potential. If you stay on top of the chemicals, it might help - but I think the empty space at the top would still be prone to corrosion. Have read lots of bad stories about some OWBs corroding out at/around the water line.

We also still don't know much more about other system details - such as elevation difference between the bottom of your tanks & the top of your boiler. But the fact that you bulged your tanks just from having your circ running (I think I read that right) would make me quite apprehensive.

Not sure I'll be able to add much more to this one.

The elevation difference is about 4 feet from the top of the tanks to the bottom of the boiler. I know I need to vent the tanks. The only thing that concerns me is, when the boiler circulator is running, wouldn't it just push water up the vent line to a certain point? This would cause low volume in the boiler and require more water to be added?

Here is a crude drawing of the boiler and tanks
[Hearth.com] My first wood boiler, storage and data monitoring
 
You need to vent your tanks to equal height of the boiler vent or your water from your boiler will just push out the lower storage tank vent from gravity. So just run a piece of pex up to the same height or higher then your boilers vent and you're good.

I know you said you bought the fuel oil tanks because they fit into the basement, my question is you couldn't find anywhere that had any type of pressure vessel tank (propane, air, etc.) That could fit at all? My only concern on your system is the thin walls of your fuel oil tanks rotting out in a few years. Even with proper maintained Chem levels the tank walks are still very thin. Especially if you use that foam insulation. You may get a small leak in the wall or bottom of your tank that you might not realize, then one day you have a soggy basement floor.

Not trying to beat you down just food for thought is all.
 
You need to vent your tanks to equal height of the boiler vent or your water from your boiler will just push out the lower storage tank vent from gravity. So just run a piece of pex up to the same height or higher then your boilers vent and you're good.

I know you said you bought the fuel oil tanks because they fit into the basement, my question is you couldn't find anywhere that had any type of pressure vessel tank (propane, air, etc.) That could fit at all? My only concern on your system is the thin walls of your fuel oil tanks rotting out in a few years. Even with proper maintained Chem levels the tank walks are still very thin. Especially if you use that foam insulation. You may get a small leak in the wall or bottom of your tank that you might not realize, then one day you have a soggy basement floor.

Not trying to beat you down just food for thought is all.

From what info I have found, the boiler is made of 10 gauge. The tanks are made of 12 gauge. As long as I'm diligent with my chemicals, I should be able to get a few years or so out of them. The plan is to eventually add an outside entrance into the basement, and do two 500 gallon propane tanks. I will add a vent line, then see what happens with regards to expansion. Even at a 4% expansion, I think I will need about 30 gallons of space. I will just need to find a place that I can make room for the tank, that is higher than the lines for my loops, and lower than the vent on the boiler.
 
With 4 feet of elevation from top of tanks to bottom of boiler, then adding another 4 feet of height for each of the tanks & boiler (a guess), that would make about 5 psi of pressure at the bottoms of your storage tanks just from standing water with no added forces. I don't have an oil tank any more, but I'm pretty sure the stamp on it re. pressure was something like 2.5 psi? Could be wrong - but it doesn't take much pressure to pop such a tank, as has been seen with the bulge. There's likely some wiggle room in there, but I'd still be apprehensive..
 
Do you have any piping or heat emitters above the boiler? If so, that section will run at sub atmospheric conditions. Here is an example of how that calculation works.

Also the PONPC is an open system is right where the air and water meet at the top of the boiler.

The Taco pumps should be rotated so the motor is not pointing up, to assure you have fluid at the bearing.
 

Attachments

  • [Hearth.com] My first wood boiler, storage and data monitoring
    Screen Shot 2016-08-10 at 4.57.23 PM.webp
    57.5 KB · Views: 415
  • [Hearth.com] My first wood boiler, storage and data monitoring
    Screen Shot 2016-08-10 at 4.57.40 PM.webp
    108.7 KB · Views: 578
  • [Hearth.com] My first wood boiler, storage and data monitoring
    Screen Shot 2016-08-10 at 5.00.38 PM.webp
    181.9 KB · Views: 425
  • [Hearth.com] My first wood boiler, storage and data monitoring
    Screen Shot 2016-08-10 at 5.00.51 PM.webp
    92 KB · Views: 385
Do you have any piping or heat emitters above the boiler? If so, that section will run at sub atmospheric conditions. Here is an example of how that calculation works.

Also the PONPC is an open system is right where the air and water meet at the top of the boiler.

The Taco pumps should be rotated so the motor is not pointing up, to assure you have fluid at the bearing.

The boiler is the highest point, as in none of the loops go above the top of the boiler.

I did not know that about the circulators. I will turn that when I drain the system to add my vent and expansion tank.
 
I'm having trouble figuring out what height to mount the expansion tank. since the tank will be straight through and be part of the vent line from the storage tanks, if I go too low below the water line in the boiler, it will just fill with water from the boiler and even itself out. If I go too high, the water would just come out of the vent on the boiler. Best I can come up with is mounting it horizontally with a small portion of the tank below the water line of the boiler. I figure at best, the top of the tank needs to be below the vent of the boiler.
[Hearth.com] My first wood boiler, storage and data monitoring
 
I'm half in the dark here, having no experience with an open system - but my simple thinking has me asking why not simply put the expansion at the boiler vent? I'm not understanding why it needs to be plumbed into the top of storage. That would also help reduce or eliminate the corrosion-prone air space in the boiler - but would likely add some height & static pressure to the system, I guess. Or if not at the vent itself, then tied otherwise to the boiler.
 
I though about that but, I would have to do some serious rigging to put it up on top of the boiler, and I don't want to make it an eye sore. I'm debating extending the vent up higher on the boiler, that way the expansion tank can be bottom positioned at the top of the cold water line, and still take on the expanding water, without overflowing the boiler.
 
Simply out of ignorance, could you tell me why it needs that vent tank at all? What is the difference in volume at 160 degree vs 180(the boiler temp differential settings)? Can be more than a few gallons I would think. Couldnt you just let the boiler blow out the extra water from the top vent on the boiler the first time it fires, then it would just run with that amount of water. If you cooled the boiler down to 140 or less for some reason you might have to add some water.
 
Please call someone from B+G or Taco and ask to
have a field representative come to your place
to look at your system.

They deal with large volumes of water for hydronic storage in
heating and cooling as a business for large buildings and skyscrapers.

At most you may have to move the tanks to the garage
and use them to buffer the water storage temperature
in the boiler to avoid further damage to the tanks.

If you put the tanks in the garage they will be higher
in elevation and be subject less pressure from the
water weight in the boiler.

You can always have a vent stack with an upside down U to
vent teeing both tanks together with one vertical pipe

A steel expansion tank must have a sealed system storage to
work properly with a sealed air cushion above the water line to allow
the air bubbles to migrate to the air pocket and slowly dissolve in the water column.
 
How many gallons total? You need to calculate the expansion volume for the fill water temperature, to max temp, maybe 60- 190F operating range. You cannot calculate from 160- 190, if it goes off and drains to ambient temperature you will have a low water condition in the boiler. Water both expands and contracts.

How much expansion space is in the boiler itself, generally they have space for expansion for at least the volume of the boiler itself. Adding those buffer tanks may require additional expansion room.

The Wessel Tank website has a sizer for calculating tank volume, the boiler manufacturer should know the expansion available in the unit.
 