Question:
How many pounds of pellets should this house burn per day?
Pellet usage with the OAT connected in the basement reading about 65°:
Test One: 33hrs, 160lb pellets burned, (160lb pellets / 33hrs =4.84lbs pellets per hour) 2.9 bags in a 24 hour period. The temperatures during this test were between 1° and 22°.
Test Two: Pellet usage from the December 22nd start-up. 6.13lbs Per Hr 3.5 bags per day. We have only had a handful of days with temps below 20°
Home:
36’x 28’ Two Story 1872 square foot Cape Home, 2x6 R13 wall construction.
Heating Systems:
(Secondary) New Yorker Boiler FR 98 W, (Net out-put 82,000BTU) 710 gallons annually
(Primary) Harman Pellet Boiler PB 105, (Net out-put113,900BTUH) (connected parallel)
Hot water base board 2 zones (53’ base board 1st floor & 32’ base board on 2nd floor)
Hot water coil in the Oil Boiler for domestic hot eater
Thermostats set at 68° 1st floor & 67° on the second floor
Heat Loss Calculations:
Building Envelope Heat Loss 16,462 BTU/hr
Infiltration Heat Loss (based on average of 0.5 ACH) 13,071 BTU/hr
Total Heat Loss 29,533 BTU/hr
Total Output 36,916 BTU/hr
Total Input 46,145 BTU/hr
How many pounds of pellets should this house burn per day?
Pellet usage with the OAT connected in the basement reading about 65°:
Test One: 33hrs, 160lb pellets burned, (160lb pellets / 33hrs =4.84lbs pellets per hour) 2.9 bags in a 24 hour period. The temperatures during this test were between 1° and 22°.
Test Two: Pellet usage from the December 22nd start-up. 6.13lbs Per Hr 3.5 bags per day. We have only had a handful of days with temps below 20°
Home:
36’x 28’ Two Story 1872 square foot Cape Home, 2x6 R13 wall construction.
Heating Systems:
(Secondary) New Yorker Boiler FR 98 W, (Net out-put 82,000BTU) 710 gallons annually
(Primary) Harman Pellet Boiler PB 105, (Net out-put113,900BTUH) (connected parallel)
Hot water base board 2 zones (53’ base board 1st floor & 32’ base board on 2nd floor)
Hot water coil in the Oil Boiler for domestic hot eater
Thermostats set at 68° 1st floor & 67° on the second floor
Heat Loss Calculations:
Building Envelope Heat Loss 16,462 BTU/hr
Infiltration Heat Loss (based on average of 0.5 ACH) 13,071 BTU/hr
Total Heat Loss 29,533 BTU/hr
Total Output 36,916 BTU/hr
Total Input 46,145 BTU/hr