From the manual
4 Flashes: Missed Ignition During the ignition sequence the load does not ignite.
The unit will automatically retry once from the first failed attempt. Fuel No fuel Hopper Empty Feed Jam Feed doesn’t turn Feed motor disconnected or failed
Firepot: Firepot Dirty so fuel is not near the ignition hole in the firepot
Igniter: No power Debris in the end of the igniter chamber
Fill the hopper Inspect and clear jam in the feed tube
Inspect the feed motor circuit (hopper lid must be closed, vacuum switch must be closed (ie exhaust blower on), and feed motor must be plugged in. Clean the firepot Check leads and if the igniter works. Clean the end of the igniter chamber from inside the firebox (removal of the firepot is required for this step).
 
pelpro 60 .4 red flashes
Need a little more info.

Does it light, but then not feed pellets resulting in a missed ignition code. I’d do it very easily could be ash build up in the exhaust that is insulating the proof of flame sensor.

Does it feed pellets into the fire pot, but not ignite. If so I would start with looking at the igniter.

If the auger doesn’t feed pellets, then check and make sure it is getting voltage.