I don't talk much on the forums. I do cruise them a lot when i have problems. I have been having the same ongoing problem with my stove since the end of last years heating season, to a few hours ago, and thought i might share.[
Ok, my furnace was working, but it wasn't heating well, and was going through way more pellets then it ever has before. I replaced the esp, i replaced the (insanely expensive) circuit board. I checked all the gaskets, and doors, I tried adjusting the exhaust fan to a lower setting. I even switched my fan limit switch to a known good switch just to be thorough. Sometimes on cold nights it wouldnt heat over 66 degrees.....The problem is that my exhaust blower is blowing to fast. there is to much airflow across the fire box, and it causes a pressure switch to not let the feeder turn. As the firebox changed temps it changed the suction in the firebox and wold cause the feeder to work sometimes, and not sometimes.
I finally figured that out, and a few days ago i was thinking about the air intake on the unit, and came to the conclusion that the smaller hose might create enough restriction in airflow to slow down the exhaust fan, thus fixing the problem, so i tested my theroy, and it seemed to help, but still not work exactly right. So i put aluminum tape over the air intake opening till the system seemed to work correctly (in my case it almost complety covered the air intake). That worked well for a few days so today i cut a cap out of metal that fit snugly over the air intake. Then i cut out almost half of the cap so it left half of the air intake hole open... Then i cut another circle the same size of the cap and cut a hole about half the size in it. Then i bolted both together so i could adjust the air intake as needed. The pf100 seems to be working better then it did when it was new.
There is a very easy way to see if this is your problem. Turn the breaker at the bottom of your machine off, then turn your feed rate to 6. Then makre sure your thermastat is calling for heat (atleast 4 degrees higher than the temp in your house or more). Turn the breaker back on and give it a few seconds. Then just put your hand over the air intake, and if your feeder starts turning, then that is your problem. note... it should only take a few seconds for your feeder to begin turning, and keept turning.
If anyone wants pics of what i did to fix mine, ill will send them some or post them here. I might be persuaded to make a few to send out, (for free) as long as i have the extra metal and the time to make them.
Anyways this particular problem has taken me a long time to figure out so i thought i would share it with anyone else with the same un-informative piece of junk owners manual, and absolutly no customer support from harman. And in my area there isn't a qualified service tech for 100's of miles. So to those of you who are considering one for the main heating source in your house, I would cation you to do your homework and make sure you have someone qualified is near. Even if you are pretty handy, there is always something that can happen that could take awhile to figure out, esp with there being no official information about how this system is supposed to operate. Thats just my 2 cents..
Ok, my furnace was working, but it wasn't heating well, and was going through way more pellets then it ever has before. I replaced the esp, i replaced the (insanely expensive) circuit board. I checked all the gaskets, and doors, I tried adjusting the exhaust fan to a lower setting. I even switched my fan limit switch to a known good switch just to be thorough. Sometimes on cold nights it wouldnt heat over 66 degrees.....The problem is that my exhaust blower is blowing to fast. there is to much airflow across the fire box, and it causes a pressure switch to not let the feeder turn. As the firebox changed temps it changed the suction in the firebox and wold cause the feeder to work sometimes, and not sometimes.
I finally figured that out, and a few days ago i was thinking about the air intake on the unit, and came to the conclusion that the smaller hose might create enough restriction in airflow to slow down the exhaust fan, thus fixing the problem, so i tested my theroy, and it seemed to help, but still not work exactly right. So i put aluminum tape over the air intake opening till the system seemed to work correctly (in my case it almost complety covered the air intake). That worked well for a few days so today i cut a cap out of metal that fit snugly over the air intake. Then i cut out almost half of the cap so it left half of the air intake hole open... Then i cut another circle the same size of the cap and cut a hole about half the size in it. Then i bolted both together so i could adjust the air intake as needed. The pf100 seems to be working better then it did when it was new.
There is a very easy way to see if this is your problem. Turn the breaker at the bottom of your machine off, then turn your feed rate to 6. Then makre sure your thermastat is calling for heat (atleast 4 degrees higher than the temp in your house or more). Turn the breaker back on and give it a few seconds. Then just put your hand over the air intake, and if your feeder starts turning, then that is your problem. note... it should only take a few seconds for your feeder to begin turning, and keept turning.
If anyone wants pics of what i did to fix mine, ill will send them some or post them here. I might be persuaded to make a few to send out, (for free) as long as i have the extra metal and the time to make them.
Anyways this particular problem has taken me a long time to figure out so i thought i would share it with anyone else with the same un-informative piece of junk owners manual, and absolutly no customer support from harman. And in my area there isn't a qualified service tech for 100's of miles. So to those of you who are considering one for the main heating source in your house, I would cation you to do your homework and make sure you have someone qualified is near. Even if you are pretty handy, there is always something that can happen that could take awhile to figure out, esp with there being no official information about how this system is supposed to operate. Thats just my 2 cents..