Woodfarmer1

Member
Nov 10, 2013
247
Bowmanville, On,Can
I have a munchkin condensing boiler that won't fire, the code says the pressure is low. The wood boiler runs the P/S at 20 psi, and when it's hot the propane runs up to 15psi, but as the wood burns out and the P/S cools to less than 100* (which is where the propane boiler aqua stat is set) it won't fire and the pressure at the prop boiler drops to zero?

I can't find any leaks in the system and even closed the air bleeder valve with no luck
 
I wonder if your expansion tank is flooded or if it is adequately sized.
 
I agree with Fred, I would check the expansion tank. I also run a Munchkin for backup. I only run into the low pressure situation in the spring when I shut down my Eko 25.

Good luck
 
i put a gallon of water into the system and this brought the pressure up to 24psi and the boiler fired
 
Good news, my Munchkin fires with 10 PSI on the gauge, I thought I read that the pressure switch was looking for 12 PSI.
 