Way back in 2008(!) I sketched up a system plumbing schematic that became a sticky. It's been a while, and I've worked out a few other designs and variations since then. I'd like to take my current thinking and pass it by the collective wisdom of the boiler room wizards. Does this approach make sense, and does it accomplish the objectives listed below? Have I missed anything important? Looking for any thoughts, ideas, and suggestions.
Thanks....
Notes:
Key objectives and ideas:
Thanks....
Notes:
- All circulators have integral check valves.
- In this version, the bypass circ is a Taco Viridian or other temperature controlled variable speed circ, set to maintain 140 degrees at the wood boiler inlet whenever the wood boiler is operating. A Danfos or equivalent mixing valve could be used instead.
- The Load Circ and Oil Circ are Grundfos Aplhas or other constant pressure circulators.
- The wood boiler circ could be a Viridian or other variable speed circ set to achieve the desired target temperature at the wood boiler outlet. It could also be a fixed-speed circ controlled by the boiler controller.
- The oil boiler is disabled when the top of storage is hot enough to be useful.
- The load circ is disabled when the storage top is not hot enough to be useful.
Key objectives and ideas:
- The wood boiler / storage loop on the left side is completely independent from the loads on the right side.
- There's no opportunity for 'ghost flow'.
- The oil boiler will never charge storage.
- Each side (wood boiler and loads) can use different flow rates as needed to optimize performance.
- Stratification in storage is easily maintained.
- Controls can be very simple - native oil boiler and wood boiler controls plus a thermal switch on storage to disable the oil backup and enable the load circulator.
- Wood and oil are independent. Either can be valved off and worked on without losing heat.