Simplest Pressurized Storage System Design

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

Nofossil

Moderator Emeritus
Hearth Supporter
*** NOTE: You cannnot reply to this thread. If you have questions or comments, please create a new thread ***

This topic has come up many times, and I don't think I've been able to explain this well enough. Here's an attempt to explain storage plumbing and control for the simplest and most bulletproof design that I've been able to come up with. Bottom line: Storage does not have to be complicated.

I've chosen a simple parallel wood / oil system with zone valves as an example. There are plumbing and control wiring schematics for both before and after storage. The same basic approach would work with other system designs such as systems that use a circulator for each zone rather than a zone valve.

In this system, each boiler has a circulator that runs whenever that boiler is hot. That's normal behavior - no changes are needed. These circulators need to have check valves to prevent reverse flow.

Each heating zone has a zone valve that's controlled by the zone thermostat (or aquastat in the case of the indirect DHW that I've shown). This is also the normal configuration - no changes are necessary.

Zone valves have built-in limit switches that close when the zone valve is open. Normally those contacts are wired in parallel and connected to the oil boiler demand input. Here, we have to make some changes.

First, the zone valve limit switches are removed from the oil boiler demand input and connected to the 24vac thermostat transformer (see schematic).

Second, we need a 24VAC relay that we energize when any of the zone valve limit switches are closed. This relay will turn on the Load Circulator.

Third, we need a 24VAC relay for the oil boiler demand input - when this relay is energized, it creates a closed circuit that turns on the oil boiler. This takes the place of the zone valve limit switches.

Finally, we need an aquastat at the top of our storage with contacts that close only when the storage temperature drops below the minimum usable temperature - we'll say 140 degrees for this example. The signal from the zone valve limit switches passes through this aquastat before going to the oil boiler demand relay. In that way, if the storage is above 140, the oil boiler will not come on when the zones call for heat.

Theory of Operation

1) Heating from storage
If there is any heat demand, then the corresponding zone valve(s) are open and their limit switch(es) are closed. This energizes the Load Circulator. If the storage is above 140, and the wood boiler is cold, then the load circulator will draw hot water from the top of the storage and return cool water to the bottom of the storage. At this point, there is a clockwise loop from storage through the zones and back. There is no flow through either boiler.

2) Heating from Wood Boiler
If the wood boiler is fired up, then the wood circulator will come on. If there's still demand, then the load circulator is still running and the bulk of the flow will be from the wood boiler through the zones and back. Depending on the relative flow rates of the two circulators, there may be some flow into or out of storage.

3) Heating storage from the wood boiler
If the wood boiler is running and there's no demand, then the load circulator is off and there is no flow through the heating zones. In this case, the flow is from the wood boiler clockwise to the top of the storage and back from the bottom of the storage to the wood boiler.

4) Heating with oil
If there's demand from one or more zones and the storage is below 140, then the storage aquastat contacts are closed. This passes the zone demand signal to the oil boiler demand relay, which will turn on the oil boiler. At this point, the primary flow is from the oil boiler through the zones and back to the oil boiler. As in the case with the wood boiler, there may be some small amount of flow into or out of storage based on the difference in flow rates between the oil circulator and the load circulator. This should be minimal and not be a big concern.

With this approach, storage adds one circulator, one aquastat, and two relays. The system does exactly what you would want - heat from the wood boiler supplies zone demand first, and heats the storage whenever there's excess heat produced. Heat demands are satisfied by wood if it's running, then by storage if it's available, then by oil as a last resort. No additional controller is needed.

Components

There are no components that are particularly specialized. The relays, aquastat, and circulator can be obtained almost anywhere. If you have the time and inclination. eBay is a great source.

Any 24vac relay that can switch a couple of amps will work fine - Omron's LY2-AC24 (sold by Digi-Key as Z-788-ND) for example - they're about $8 each, and you can get plug-in sockets for them that simplify connections.

The aquastat needs to be a break-on-rise model. For example, the Honeywell L6006A1145 would work well, and it has an adjustable differential temperature. It's about $80 from PexSupply and other sources. Installing a well for it is an exercise left to the reader.

The load circulator should be similar in size to the existing circulator(s), or smaller if the heat loads are much smaller than the output of the boiler.

I hope this helps. Comments, feedback, and improvements are welcome as always.
 

Attachments

  • [Hearth.com] Simplest Pressurized Storage System Design
    storage-controls-before.gif
    9.5 KB · Views: 18,464
  • [Hearth.com] Simplest Pressurized Storage System Design
    storage-controls-after.gif
    14.3 KB · Views: 21,081
  • [Hearth.com] Simplest Pressurized Storage System Design
    parallel-no-storage.gif
    16.3 KB · Views: 24,874
  • [Hearth.com] Simplest Pressurized Storage System Design
    primary-storage-loop.gif
    19.6 KB · Views: 26,242