SCFA said:
NY Soapstone said:
Quick update to this thread... as of 5PM today, we made our first bit of solar hot water with the new system for a couple hours... amazingly, we were running until 7PM which is nearly dark this time of year up here! Of course the solar tank was also at groundwater temperature, so pretty easy to get some gain going to the roof for those couple of hours
Tomorrow is looking like great weather to charge up the 120 gallon tank - many more details to come in a new thread once we get some pictures and experience.
-Colin
NY Soapstone, I did a quick search and couldn't find the new thread for this. any updates? thanks, i'm looking to do a similar setup.
Hi -
Yea, I know an update is long overdue... but this time of year we don't have tons of production of interest.
In general, we have just been preheating the groundwater prior to going into the tankless coil - it will likely be March or April before we go to 100% solar. But, some observations that may or may not be of interest...
Through October, it was hard for us to gauge performance because it was just using a differential controller and we had no idea how long it ran or what the tank temperature was. It was warm, but not hot. Since then, we have also taken down a tree that was responsible for significant shading in the mid afternoon - something we knew we had to do anyway because it was rotten, and this was recommended during the site survey. (see other thread for pics
That will make a significant improvement as we go into spring as that is peak production time with our orientation.
We finally got the temperature readout installed in early November. During this period, the 120 gallon tank would be about 70 degrees, vs incoming groundwater in the low 50s. At most, the solar system would run 3-4 hours/day - it would shut off quite a bit earlier than in October due to the lower temperatures and poorer sun exposure - we still had the tree blocking some sun as well.
By December, it was getting up to around 58-62 depending on the weather. On a typical day in the 40s with mostly sun, the system runs about 2 hours, and produces about 10,000 BTUs/hr while running. So not a ton of heat this time of year, but it has still let us get away with lower temperatures on the central boiler since the water is coming in a bit warmer than normal.
Estimating for those two months based on hours of operation logged by the controller, we put 750,000 BTU into the water in Nov; 350,000 in Dec. Assuming about 70% efficiency on the oil burner transferring heat into the water, it would have taken about 11.4 gallons of oil to generate the same heat in the boiler.
This is remarkably close to our projections - believe it or not, when I did our payback analysis, I had projected saving 12 gallons total between Nov/Dec, although the way I got to that number was a little different!
Obviously this trend will start reversing again now going into longer days and higher sun angles and we will see things increase substantially going into spring, and the elimination of a tree will make a big difference.
One other thing I should also mention is that our panels are closer to WSW rather than due south and at 30 degree incline. This means that we don't anticipate a lot of winter production, but as the sun comes back up, we will see a substantial increase - I can tell a marked difference between October and December, for example. Our goal is to shut down the boiler altogether for 6-8 months when we don't need backup heat - will not be able to determine that for sure until March or April. That is key to the payback since you eliminate all hot water demand use and standby losses - anything you get in winter is just a nice bonus. Once we shut down the boiler, the combination of saving all standby losses as well as hot water production costs works out to about $75/month at current oil prices. If you really wanted higher winter production, you would want to mount them on a south facing roof at a higher angle. In our case, the location chosen sacrifies a little winter production for the fact that they are nearly impossible to see driving or walking up to the house - something we felt was important for resale someday. And no matter how you orient, the big production/savings comes from the spring-fall period.
If you have any specific questions, I would be glad to answer them - I worked with the installer throughout the job so most all of it I am familiar with.
I also have a spreadsheet that may be useful to illustrate what we looked at as part of the decision process - will try to post it sometime. It is a much harder case to make if you are using a natural gas hot water heater, or have cheap electric rates, for example; a tankless coil system is one of the easiest to make the economic case.
-Colin