Last edited:
(Separator tank is "this tank".)
There would be little point in running the separator-tank-to-house-loop-circulator constantly. Normally only need to run when there is a call for heat. (If you want to get fancy you can use an aquastat on the return side of the water-to-air HX that disables the furnace fan until the coil is hot.)
Zone valve is not needed.
1.25" pipe feeding separator tank is likely much bigger than it needs to be.
Controlling storage-to-separator-circulator with an aquastat near the center of the separator tank, or lower, should work well. The range can probably be much tighter than 140-170. I think something like 140-141 would do the trick, maybe higher setpoint but still a tight range in the dead of winter.
If there is more head on the storage-house circuit, than boiler-storage circuit (say, smaller piping, more fittings, plus all the hx's), then the water should go the path of least resistance when the boiler circ is running. Orienting the T's so the straight shot is between the boiler & storage & direct to storage would also help. Along with having it be uphill from boiler right into storage. Maybe combined with having some downhill from storage to house. Imagine with no pumps & designing for convection between the boiler & storage.
Constant flow can defeat storage - good stratification optimizes storage capabilities. May be worth it to do manifolds in the house so you can parallel your loads & pump on demand.
Finer details also sometimes get lost in 2d drawings. Are those storage tanks stacked or side by side? The pipe going into the top one should be at the end opposite the one leaving it at the bottom. Also thinking the ins & outs of the separator tank should be at top & bottom - no direct experience with separators though. Also not sure how much benefit it would be in this application - usually they are used for multiple loads with varying temp requirements. And/or supplies with varying supply temps (like incorporating solar). I think - again, no direct experience, someone can correct if wrong on that.
Do you know from having run your existing system how low your supply temps can be & still maintain house temps?
85 views and no comments. Did I say something wrong?
I understand constant flow hurts storage, which is the reason for the separator tank. That tank will be around 150 gallons and I do not consider it storage, I want that tank to mix. In my mind the separator tank/house circuit is 1 large zone.
Forgive the drawing it is mostly a copy of Nofossils simplest pressurized storage with the addition of the separator circuit. Many details were left out as far as storage size, orientation, valves, air separators ect. The orientation of the tanks is still unknown. Storage will either be a single 1000 gallon tank or 2 500's hoping to set them vertical. I would prefer them vertical not sure if all the extra work would be worth it vs a single 1000 horizontal.
During the coldest part of winter I can heat with 140 water. I can maintain all the way down to 100-110.
I wasn't studying your diagram closely enough. To eliminate the zone valve, need to move connection point for the separator supply line pretty close to the top of storage.How would the boiler charge storage without the zone valve?
Then hire a steamfitter to weld in some 4" or bigger, just to be sure.As far as pipe size, I always thought bigger was better.
So with the big pump running all the time how will your hottest water from the boiler ever get into the storage tanks?
I'd have the cold return to storage and delete the pump between storage and what you currently call the separator.
I would like you to invest in a 2 paperback books "Pumping Away" and "Classic Hydronics"
written by by Dan Holohan. He writes his books for the layman and plumber alike and makes
his writing easy to understand and fun to read with many many actual examples he has
encountered and corrected many plumbing mistakes made by plumbers and home owners alike
in many years of being in heating business where he preaches simplicity in design and how to
control central heating and cooling systems.
If I remember correctly there is a design in the "Biomass-Hydronics-Training PDF" in the sticky threads that shows a design that uses gravity to feed a separator tank.
I'm not sure that mixing tank will benefit.
Circ 2 would cycle on and off via the aquastat in the seperator tank which is why it would be set with a large differential.I am thinking that if circ 3 runs constant, then circ 2 will be also. Or very nearly so.
Tank verticallity?
Low flow rates on the load circuit also help.
A good deal of this depends on the characteristics of the house stuff, which we don't know much about. Are you sure on how much flow you will be needing to the house? Amount of time it is running doesn't really mean much without correlating with GPM. And delta T. Do you know how many GPM you're pumping while maintaining temps now?Might also be worth investigating upsizing your HXs. Maybe even adding some hydronic rads if you have places you could do it easily. If you can lower the flow needed and widen the dT through the house, the situation would improve.