Stove not responding to thermostat

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

mizzer

New Member
Oct 9, 2014
4
Ohio
I think I have the Sterling 8521. It's about 15 years old.

I've had trouble with it in the past: I could not get the stove to light if the switch was set to t-stat. Technician took some readings. Everything seemed fine. While he was here it started working. Go figure. Cost me $85 for essentially nothing. That was two years ago.

Fast forward to now. The stove lights when set to "on" AND when set to "t-stat". Thing is I cannot get it to turn off when the rocker switch is set to "t-stat".

Things I tried:

1) Cleaned t-stat.
2) Replaced batteries in t-stat.
3) Reconnected wires from t-stat to stove.
4) Replaced wires from t-stat to stove.
5) Replaced 3-way rocker switch.
6) Completely removed t-stat from circuit.

I've reseated almost every wired connection.

Other things of note:
1) I can short the connection on the rocker switch and the stove will light (when set to "off").
2) If I pull the (I assume) hot wire from the switch (from the t-stat) I can then touch it to the back of the switch and it will light. This happens whether or not the t-stat is connected.

Could it be a bad thermopile?

Any ideas would be great.
 
What kind of tstat are you using?
Replaced batteries...
Did you TEST them with a multimeter?
Thermopile is not the problem...
When a thermopile goes south, a stove will not STAY on if it even COMES on.
 
What kind of tstat are you using?
Replaced batteries...
Did you TEST them with a multimeter?
Thermopile is not the problem...
When a thermopile goes south, a stove will not STAY on if it even COMES on.

Hunter 42999B, I've been using it for 10 years.

Remember: I removed the t-stat from the circuit (took it off the wall) and the problem remained.
 
OK. What happens when you take the wires OFF the thermostat & touch them together?
Does the unit come on?
What happens when the wires are pulled apart?

Edit: What happens when you jump the terminals Labelled TP-TH (or TH-TP) & TP?
If the unit comes on, then there's an electrical problem (wiring or switch) somewhere. (DOH.)

Brain F*rt: TH - TP & TH are the correct terminals to jump. Sorry.
 
Last edited:
OK. What happens when you take the wires OFF the thermostat & touch them together?
Does the unit come on?
What happens when the wires are pulled apart?

Edit: What happens when you jump the terminals Labelled TP-TH (or TH-TP) & TP?
If the unit comes on, then there's an electrical problem (wiring or switch) somewhere. (DOH.)

Good ideas. I will try this when I get home and report back.
 
Jumped TP-TH and TP = nothing
Jumped TP-TH and TH = unit lights

Pulled apart wires = no effect, same problem
 