Thermostat on enviro

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

Cedarjunki

Minister of Fire
Oct 17, 2015
513
Upstate NY
2008 enviro evolution (ef5)
Has the 3 selector switch on the control panel.
Auto/hi-low/manual

If i connect a wall thermostat, can i still switch between the auto and manual modes? I notice the thermostat connection on the board has a jumper wire like most. So i am curious if i would need to replace the jumper if i decide to run in manual mode at times?
 
If it is the same as the M55 function, you can run it in manual just by the switch. If your thermostat has an on/off function, you can pretty much use it to run in manual (on will lock it in the hi heat setting, off will be the Lo)
 
So in order to have it actually run in manual mode i would need to crank the thermostat up to a high setting to keep the circuit closed. Otherwise even with the switch on manual it would only run on low.

I just thought they would use a switch that would actually act as the jumper while being in manual mode.
 
No, switching it to manual will run in manual and the thermostat will do nothing, you set the heat level on the panel.
I was just pointing out that you can use the thermostat in hi/Lo mode to lock it in either hi or Lo, similar to the manual setting where it will run constant in either of those levels
 
No, switching it to manual will run in manual and the thermostat will do nothing, you set the heat level on the panel.
I was just pointing out that you can use the thermostat in hi/Lo mode to lock it in either hi or Lo, similar to the manual setting where it will run constant in either of those levels

Maybe this one is set up diff. As it sits, they have the thermostat wires from the board looped together. If i hook them to the thermostat the circuit would then be open until the thermo calls for heat. So if only flipping the switch would allow to manually control the heat settings why is the thermostat wires tied?

I am playing with it to figure it out. Was just hoping for easy answers
 
if you mean the jumper wire, i believe you are supposed to remove it if you install the thermostat. page 19

http://www.enviro.com/images/manuals-brochures/owners-manuals/C-11142 Instruction Evolution EF5 Domestic Technical Manual.pdf


Yes i know about removing the jumper. I used a thermostat on my old stove. But this one has short leads instead of a jumper. But regardless, they are tied together so they are a jumper.
The thermostat connection needs to have that jumper installed in order to have control of the heat settings in manual mode. If i connect a thermostat, manual mode does not exist just by flipping the switch. Either i would need to crank the thermostat to act as a jumper or install the jumper back on the board.

I still think they would have used a better switch allowing the manual mode selection to act as the jumper.
 
I dont know maybe i just cant describe the situation clearly enough.. i have read the manual. I have the manuals in paper. I know how the controls work.

Without the jumper the stove will only work on low. With the thermostat installed, unless it is calling for heat that circuit is open wether the switch is in manual mode or not. In order for manual mode to have control over the stove that jumper needs to be in place. I dont think having to crank the thermostat or installing the jumper should be necessary when there is a switch for manual mode. Not a huge problem i guess. Just could be a better design where the manual selection on the switch actually created the jumper required.
 
Ok so i have confirmed my theory. If i have the thermostat connected, regardless if it is on or off, switching the stove to manual does nothing without cranking the thermostat or reinstalling the jumper.

If i only switch it to manual mode then it only feeds at the low setting.
 
Status
Not open for further replies.