I lost track of the thread but someone asked if I could document temp drops in various installations that we have done or been able to document.
I had a chance to visit a couple this past week and the numbers are posted below. I'm going to try to keep track of this post and add to it over the next few weeks. All temps were measured with a Fluke digital thermometer using a strap on thermocouple and taken on bare steel or copper piping.
Install #1 This installation consists of a 235' trench with supply and return being 1.5" Wirsbo pex. The tube was buried to a depth of about 25-30" and runs directly beneath about 55' of residential driveway. It was insulated with sprayed closed cell poly urethane foam to an average thickness of 3". Flow rate in the pex is calculated at 12.65GPM. The soil type is very light sand.
Temp at point of entry to supply 151*
Temp at point of entry to house piping 150*
Temp at point of return in house 144*
Temp at point of return to boiler 145*
I found this to be very interesting because the return pipe actually picked up a degree traveling back to the outbuilding in which the wood boiler is located. It would appear that there is no actual heat loss underground as that 1* of measured temp drop measured is being transferred to the return tube.
Install #2 This installation consists of 108' of trench and uses the generic 1" pex product wrapped in 1/4" foil/foam a few times and inserted in black corrugated drain tube. Approximate depth is 48" and it runs through normal sandy loam type soil and is in an area which can get damp seasonally. Calculated flow rate is 6.3 GPM
Temp at point of entry to supply 178*
Temp at point of entry to house piping 170*
Temp at point of return in house 153*
Temp at point of return to boiler 149*
The temp drop from the boiler to the house is 9* which would figure out to over 28,000 btu/hr at the calculated flow rate. Also note that the return trip drops the temp only 4* indicating that there is significant heat transfer between the supply and return pex in the tubing. If you assume that 4 degrees from the supply is actually going into the return piping on the trip back to the wood boiler you have an actual temp drop of 4* in the supply from boiler to house for an actual heat loss of about 14,000 btu's. Rough mental math would equate to a heat loss underground of approximately 2 pounds of wood per hour wasted or an extra 48 pounds per day that this owner has to process and handle.
I had a chance to visit a couple this past week and the numbers are posted below. I'm going to try to keep track of this post and add to it over the next few weeks. All temps were measured with a Fluke digital thermometer using a strap on thermocouple and taken on bare steel or copper piping.
Install #1 This installation consists of a 235' trench with supply and return being 1.5" Wirsbo pex. The tube was buried to a depth of about 25-30" and runs directly beneath about 55' of residential driveway. It was insulated with sprayed closed cell poly urethane foam to an average thickness of 3". Flow rate in the pex is calculated at 12.65GPM. The soil type is very light sand.
Temp at point of entry to supply 151*
Temp at point of entry to house piping 150*
Temp at point of return in house 144*
Temp at point of return to boiler 145*
I found this to be very interesting because the return pipe actually picked up a degree traveling back to the outbuilding in which the wood boiler is located. It would appear that there is no actual heat loss underground as that 1* of measured temp drop measured is being transferred to the return tube.
Install #2 This installation consists of 108' of trench and uses the generic 1" pex product wrapped in 1/4" foil/foam a few times and inserted in black corrugated drain tube. Approximate depth is 48" and it runs through normal sandy loam type soil and is in an area which can get damp seasonally. Calculated flow rate is 6.3 GPM
Temp at point of entry to supply 178*
Temp at point of entry to house piping 170*
Temp at point of return in house 153*
Temp at point of return to boiler 149*
The temp drop from the boiler to the house is 9* which would figure out to over 28,000 btu/hr at the calculated flow rate. Also note that the return trip drops the temp only 4* indicating that there is significant heat transfer between the supply and return pex in the tubing. If you assume that 4 degrees from the supply is actually going into the return piping on the trip back to the wood boiler you have an actual temp drop of 4* in the supply from boiler to house for an actual heat loss of about 14,000 btu's. Rough mental math would equate to a heat loss underground of approximately 2 pounds of wood per hour wasted or an extra 48 pounds per day that this owner has to process and handle.