I'm thinking about the possibility of doing injection mixing in my system vs a 3-way motorized O.R. valve. As far as I understand, I size the injection circulator and piping based on the required injection flow rate, which is in turn based on the heat load and the difference between the boiler supply temp and the system return temp.
This makes good sense with an on-demand boiler, but what about when you're taking the heat out of a large buffer tank, like my GARN, and supplying low-temp zones? If the storage temp drops down to within a few degrees of the required supply temp (outdoor reset radiant floor), then the injection flow approaches the total system flow. If the storage is hot, then the required injection flow is much less. If I size the injection circ for the highest flow scenario, then when the storage is hot, the circ is operating in the very bottom of its range--which doesn't give very good reset control, from what I've read. If I size it for a boiler temp of say 180*, then when the tank is lower than that, the system won't be able to inject enough heat. So is injection not really ideal in this kind of situation, or am I missing something?
Thoughts?
This makes good sense with an on-demand boiler, but what about when you're taking the heat out of a large buffer tank, like my GARN, and supplying low-temp zones? If the storage temp drops down to within a few degrees of the required supply temp (outdoor reset radiant floor), then the injection flow approaches the total system flow. If the storage is hot, then the required injection flow is much less. If I size the injection circ for the highest flow scenario, then when the storage is hot, the circ is operating in the very bottom of its range--which doesn't give very good reset control, from what I've read. If I size it for a boiler temp of say 180*, then when the tank is lower than that, the system won't be able to inject enough heat. So is injection not really ideal in this kind of situation, or am I missing something?
Thoughts?