stoney28

Member
Hearth Supporter
Oct 12, 2008
64
Northern NY
I've got an EKO 40 with 500 gallons of storage. Earlier this year I had a leak in the boiler which has since been welded. I've been cautious about running up the pressure since then, so I'm only running the pressure (at full temp 180F) at about 15 to 18 psi. Will this affect the efficiency of the boiler? Are there any other problems that could come up?
 
Short answer is no. Water pressure has no effect on heat transfer efficiency, as long as there is no boiling. Some boilers (Garn, Empyre, etc.) are open systems meaning they are vented to atmosphere at a high point and run at zero pressure. 15-18 psi is a good place to be at full temp.

TS
 
Short answer is no. Water pressure has no effect on heat transfer efficiency, as long as there is no boiling. Some boilers (Garn, Empyre, etc.) are open systems meaning they are vented to atmosphere at a high point and run at zero pressure. 15-18 psi is a good place to be at full temp.

TS
Thanks
 
Low pressure may not impact the boiler but are your pumps rated to run at a certain pressure? Some brands/models don't like low (perhaps sub 10) pressure.

My system holds at 12-14 psi cold. 25-26 psi typical max pressure when she's all up to temp.
 
Think I'm Ok there. Alpha specs. min 0.75psi @ 167°, 4.06 psi @ 194°. Mine is on my return line so would never, or very rarely, see much above 167°. If it did my system would have to be pretty well up to temp which would be in the 12psi range.

I did have issues with getting all the air out of my upstairs zones when I first started up with the new boiler, lots of frigging around there with hoses going here & there - but once I got those purged haven't had any more air problems.
 