Hello Q24Bubba, and welcome to the forum,
Thanks for posting the video of the start up issue on your stove. Very strange issue with the LEDs being lit in that order. Never seen it before.
Maybe it is, like you suggest, an error code. But if so, it must be a secret code to us normal consumers.The service manual has no info on error codes or how to interpret them.
But first of all: Let's think positive!
Your statement here is certainly good news:
Sometimes it takes several resets before the stove turns on and operates normally.
It confirms that most components in the stove are working perfectly.
Most likely it's the bypass relay that is ageing and showing signs of wear ( due to arcing in the internal contact set ). We've seen this issue so many times before on this forum. But not the mystical LED error code, though.
A reliable way to troubleshoot the bypass relay is to simulate exactly what it does, when it is energized by the control board during the 30 minute start up procedure. The relay simply delivers neutral to the entire stove during warm up, waiting for the low limit switch to close its contacts. Within this 30 min. period the low limit switch should have taken over, so that neutral is supplied via the low limit switch during normal operation.
All you have to do to simulate the function of the bypass relay is to temporarily jump the low limit switch ( only temporarily ! ) This is easy: Simply connect the terminals on the switch together by a jumper wire.
Caution: Unplug stove as the first thing! The terminals on the low limit switch carry full line voltage ( 120 vac/60Hz ).
Jumper wire:
The low limit switch is located on the combustion blower housing ( the component with yellow wires on the pic )
Q24Bubba, with the low limit switch jumped, does your stove start up as it should?
Good luck and take care. Keep us posted