I don't think there will be any icky water and sucking air issues with pressurized storage. Does pressurized storage also address the head issues with the 007?
Jersey Bill said:I tried to find the pressure drop of the flatplate heat exchangers, but this data wasnt readily available. does anybody have the pressure drop curves for any heat exchagers?
jebatty, you have an OWB on an open system and you say you dont have any corrosion problems with iron in your system? where is your system open? maybe chemical treatment is helping this issue.
also, in your last diagram, it looks like you are isolating the wood boiler with the heatx, not the thermal storage. But your control logic seems to work. I am concerned about the flow rates. In the case 1, all the heat from the boiler has to be pulled out by P2. with a 10 deg delta, thats 20 gpm, for 100 mbh. what size is the boiler? the pipe size would be 1.25-1.5”. Then in case 4, the same pump, and 20 gpm is going to the zone. those are big and expensive zone valves. There is also a pressure drop through the valves, and in any case, 2 valves are in series. the heatx for 20 gpm is pretty large also.
WoodNotOil said:I spoke to a rep from www.radiantheatproducts.com today and got some clearer figures and answers on this type of setup.
Corrosion
He said there is corrosion in any system whether or not it is open or closed. Bronze pumps are only needed for potable water systems. Cast iron pumps are fine in both open and closed systems so long as it is not potable.
Flat Plate ft. of Head
In my design I want to transfer the 140,000 btu output of the tarm to the storage tank and be able to draw from the tank as well through one side of the plate. At 180* feed and 160* return temps, a 30 plate exchange is needed and it would have 12 1/4 ft of head. Because my storage tank water will be pulled up by a pump and through the exchange about 2-6 ft above the the tank, we brought the total ft of head to about 15'. He said I will need 15 gpm for the correct btu transfer on the 30 plate.
Pump Size
For 15' of head at 15 gpm you would need a Taco 0010. Since this is such an expensive pump, he suggested using the Grundfos 15-58 3 speed pump on its highest speed which is about $79. My application will need two in order to pump the tank side in either direction to maintain stratification with zone valves to isolate them. I happen to have two of those feeding my zones on speed 1 that I can replace with 007 pumps. (They were part of a radiant floor package I bought when retro fitting my 1st floor) Here is a rough estimate on what the tank side setup with plate hx would be:
30 flat plate hx - $200
2 - Grundfos 15-58 - $160
2 - Zone Valves - $160
Rough Total $520
I still think that beats the price of making a coil hx. What do you think?
Would it be correct to assume that if a 30 plate HX has 12.5 ft of head that a larger, say 40 or 50 plate HX would have less ft of head. Assuming that is correct even though a larger HX will not significantly increase heat transfer, it may allow a smaller pump such as a 007 to be employed. The savings in energy costs over time could offset the cost of the larger HX. Make any sense?
jebatty said:Would it be correct to assume that if a 30 plate HX has 12.5 ft of head that a larger, say 40 or 50 plate HX would have less ft of head. Assuming that is correct even though a larger HX will not significantly increase heat transfer, it may allow a smaller pump such as a 007 to be employed. The savings in energy costs over time could offset the cost of the larger HX. Make any sense?
I think there is some confusion here. Or I'm confused. If you're operating a pressurized system, isn't it true there really is no head? It is a circulating pump, really not pushing or pulling anything, just causing a pressure differential which moves the fluid. If it's an open system, then there is head, right? Don't we need to distinguish between the two with regard to our comments?
It takes about 12 psi in a pressurized system to service a two story building. That amount of pressure will push water to about 25 feet, so if the system is 12 psi minimum in a two story structure, there is no head. See the following:
http://www.accontrols.com/documents/FeetHeadofWatertoPSI.pdf
In order to prime the system in the first place, you would need a big enough pump to overcome the height.
jebatty said:In order to prime the system in the first place, you would need a big enough pump to overcome the height.
Are you sure this is correct? As the system is pressurized by addition of water, water will fill the lower system first, forcing air to the top. With venting or a bleeder vent at the top, the compressed air will be released, allowing water to fill the entire system. The pump will not need to overcome any height, as pressure is equal throughout the system. At least this is what my "head" tells me.