4" Pellet vent size all the way up

Capernaum Posted By Capernaum, Sep 19, 2008 at 1:55 AM

Thread Status:
Not open for further replies.
  1. Capernaum

    Capernaum
    New Member 2.
    NULL
    

    Sep 7, 2008
    6
    0
    Loc:
    Philadelphia, PA.
    Is it O.K. to install 4" pellet vent pipe from the bottom connection from the appliance adapter (adapter increaser 3"-4") with 4" clean out tee and 4" pipe all the way up? Instead of going up a certain distance with 3" pipe then transitioning to 4" pipe at the 15' height point. :roll:
    my total vent height is approx. 23'.

    Thanks
     
  2. DiggerJim

    DiggerJim
    Feeling the Heat 2.
    NULL
    

    Jul 29, 2008
    497
    0
    Loc:
    Northcentral Connecticut
    Yes indeedy. You can use a 3" appliance adapter into a 4" Tee with a 3" appliance side (I have one I ended up swapping out if you'd like it) going into the 4" stack pipe. If you use the 4x3 Tee you don't need the extra adapter increaser.

    The 15' rule isn't where you change to 4" it's the total length that means you should be doing 4 & 4 all the way you can.
     
  3. kinsmanstoves

    kinsmanstoves
    Minister of Fire 2.
    NULL
    

    Aug 29, 2007
    3,471
    499
    Loc:
    Ravenna, Ohio 44266
    4" is much "gooder". Have at it.