About how much electictric power does it take to run an oil boiler?

Post in 'DIY and General non-hearth advice' started by velvetfoot, Dec 23, 2010.

  1. velvetfoot

    velvetfoot Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    6,817
    Loc:
    Sand Lake, NY
    Would a 7 amp generator do it?

    Helpful Sponsor Ads!





  2. Adkjake

    Adkjake Member

    Joined:
    Jan 3, 2010
    Messages:
    207
    Loc:
    Adirondack High Peaks
  3. burntime

    burntime New Member

    Joined:
    Aug 18, 2006
    Messages:
    2,395
    Loc:
    C'mon hunting season!
    volts x amps = watts. 120v x ??? = 1500 watts. Divide it out and you get 12.5 amps if I did that right. Nope, need a little more...
  4. North of 60

    North of 60 Minister of Fire

    Joined:
    Jul 27, 2007
    Messages:
    2,449
    Loc:
    Yukon Canada
    You will have a few things to add up for the system to be operational.
    #1) Boiler burner motor.
    #2) Your zone valves/transformer/relay loads if you have any. (they are minimal but add up if there is a significant amount)
    #3) any circulators/pumps required to move your heating medium that are on your system.
    Each device will have its own individual rating.
    All must need to be considered to have heat.
  5. velvetfoot

    velvetfoot Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    6,817
    Loc:
    Sand Lake, NY
    Thanks very much.
  6. Adkjake

    Adkjake Member

    Joined:
    Jan 3, 2010
    Messages:
    207
    Loc:
    Adirondack High Peaks
    I have a vague recollection from HS physics of a formula, WEAV. Watts = Amps X Volts

    Don't hold me to it. I'll leave it to more knowledgeable posters
  7. velvetfoot

    velvetfoot Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    6,817
    Loc:
    Sand Lake, NY
    I sort of measured it last night. I have a whole house power monitor and it looks like it takes about 270 watts steady state, with oil gun firing and one circulator. So, a 7 amp generator ought to do it, I would think, even with the startup.
  8. Later

    Later New Member

    Joined:
    Jan 30, 2009
    Messages:
    456
    My oil burner runs fine served by a 15A breaker so I'd guess that the draw is quite a bit less than that.
  9. btuser

    btuser Minister of Fire

    Joined:
    Jan 15, 2009
    Messages:
    2,027
    Loc:
    The island of Rhum Boogie
    The pumps are minimal. I forget the math but it wasn't that much, around .7amps. Relays, switches and gizmos are in the milleamp range, which I guess can add up but figure an amp for everything. You main draw is your burner, which (depends on the brand) will draw a starting wattage of around 7-10 amps, then settle down to between 2-5 amps. Your whole system is less than 10 steady amps, and probably closer to 5.

    What you may want to watch out for is if your boiler has an electronic control, it will need a better quality juice than you might think. Last year I had a tekmar 260 that wouldn't work with my genset, because the control would fire the burner, and the induction load of that motor would drag the voltage below the 5% threshold of the control. The control would konk out, shut off the burner, then come back up and start it all over again.
  10. velvetfoot

    velvetfoot Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    6,817
    Loc:
    Sand Lake, NY
    That's interesting about the Tekmar, because I have a 256 outdoor reset.
    I put a clamp on meter earlier and came up with ~4.3 amps on startup, total.
    I'll try to give it a whirl tomorrow.
  11. btuser

    btuser Minister of Fire

    Joined:
    Jan 15, 2009
    Messages:
    2,027
    Loc:
    The island of Rhum Boogie
    Its not the amperage draw but the initial voltage drop cased by the burner's motor that will cause the control to cut out. You're generator will more than likely chug through it but the control may have a hard time with it. I was in the middle of wiring mine with a plug and I was going to feed it from a small UPS , but I ended up replacing the whole boiler
  12. maverick06

    maverick06 Minister of Fire

    Joined:
    Sep 27, 2008
    Messages:
    731
    Loc:
    media, pa
    I thought about being able to run it with my generator... but it is hard wired, and I am not able to plug the generator into the house, so thats no-go for me. No big deal, still can run the fireplace!
  13. heat seeker

    heat seeker Minister of Fire

    Joined:
    Feb 25, 2011
    Messages:
    2,050
    Loc:
    Northern CT
    What some people have done is to "unhardwire" the furnace by putting a plug and receptacle in the line to the furnace. Then they can plug the furnace into an extension cord from the generator. I don't know if that violates any codes, I doubt it, but it works for them.

    FWIW, I run an oil furnace, 3 zones, and one circulator pump on a 3500 watt generator. It does grunt when the burner motor starts, but runs it all easily after that. The genny will also run our 115v well pump at the same time, so we can take showers, etc.

    The furnace has an older control on it with a few transistors in it, and it doesn't seem to mind the power dip or dirty generator power.
  14. woodgeek

    woodgeek Minister of Fire

    Joined:
    Jan 27, 2008
    Messages:
    2,798
    Loc:
    SE PA
    I believe in the last year the OP has done just that--both unhardwired his boiler AND run it on a nom 7 amp genny.
  15. Don2222

    Don2222 Minister of Fire

    Joined:
    Feb 1, 2010
    Messages:
    7,101
    Loc:
    Salem NH
    Hello btuser

    We have a Tekmar 260 for a little over a year now. It runs great with our Buderus G115WS/4 Cast Iron Oil FHW Boiler that is a Triple Pass, Cold start boiler