  1. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    I recently noticed a dripping leak on the jacket of my EKO 40, under the green casing and insulation. I took the insulation off and found the leak on a welding seam, but that's not what I'm concerned about now. The boiler itself has curve in it. (pictures attached). The level I used is just about touching the boiler in the middle, but on the end has quite a bit of space, as you can see. There is quite the change between one side of the water stain and the other. Is this normal, or is this boiler wall too weak? Anyone who's had their insulation off let me know.

    Attached Files:

    Helpful Sponsor Ads!





  2. Clarkbug

    Clarkbug Minister of Fire

    Joined:
    Dec 20, 2010
    Messages:
    1,051
    Loc:
    Upstate NY
    Hmmm, I would hope someone with an Eko can chime in and let you know. Regardless the leak is a problem. Did you buy it from a local dealer by chance? (Im thinking getting them to take a look at it). Is your T&P relief working OK?
  3. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    My T&P has never blown and I've opened it up and run it every year to make sure its working. I've got a welder coming in this week to fix the leak. That's why I took the screws out of the casing around it so I could pinpoint where the leak was. It looks like its just a pinhole at a seam. I just did this today, so I'm waiting until tomorrow to contact the dealer. I bought the stove from AHONA in 2008, but I wanted to know if this was the normal or not before I contacted them.
  4. Eric Johnson

    Eric Johnson Mod Emeritus

    Joined:
    Nov 18, 2005
    Messages:
    5,732
    Loc:
    Central NYS
    The fit and finish on those EKOs isn't the greatest, so I wouldn't be too concerned about a bulge. I seriously doubt it's anything other than a manufacturing anomaly. You're not going to bend boiler plate with 30 psi I don't think (though I could be wrong). I'd be a lot more concerned about a leak. Seems to me that's a warranty issue, for sure. How old is the boiler? How long have you had it in service?
  5. Clarkbug

    Clarkbug Minister of Fire

    Joined:
    Dec 20, 2010
    Messages:
    1,051
    Loc:
    Upstate NY
    Eric is right. I would think you would need serious PSI to bulge the boiler, but you would see other problems there too....
  6. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    I set it up the boiler in the summer of 2008, this will be my 4th winter with it. How long are those warranties for?
  7. Warranty is for 20 years. Years 1-5 at 100% At year 6 it's prorated to 60%. I'd contact new horizon before the welder does the work.

    Page 28 of the manual
    http://www.newhorizoncorp.com/PDF/ekomanual.pdf
  8. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    I bought the furnace through AHONA, is New Horizon the company that imports them from Poland, or is that the company that makes them?
  9. I just read the fine print, warranty is void if it wasn't inspected every two years blah blah blah.

    I'd still call and see what they say as this appears to be poor assembly by the maker. Doesn't hurt to mention that you will be posting there response online. Or just email them a link to this thread.

    Good luck
  10. I believe new horizon is the importer. And they are the ones that issued the warranty. Ahona, as your dealer, should be able to help facilitate the warranty repair.

    But Ahona does not sel eko's anymore so they may not be extremely motivated to help. I'd call new horizon directly if Ahona can't or won't help.
  11. Eric Johnson

    Eric Johnson Mod Emeritus

    Joined:
    Nov 18, 2005
    Messages:
    5,732
    Loc:
    Central NYS
    In my experience, New Horizon is very good about warranty issues. I'd just call Zenon directly. Maybe send photos of the leak.

    Boiler leaks are usually the tip of the corrosion iceberg in older boilers, so there's generally not much reason to start welding on them. I suppose you could corrode through a boiler in 4 years, but that would be pretty uncommon. So welding it up may work alright. But check with NH before you do anything. In the meantime, you could try to stop it with some Boiler Stop Leak. If it's just a small hole, that should heal it right up and you can use the boiler while you're waiting on the repair or replacement.
  12. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    Boiler Stop Leak? Haven't heard of that. How does that work and where can I get some? Just sent an email to New Horizon with the pictures of both the leak and the odd shape the boiler side. I'll see what comes up.
  13. Eric Johnson

    Eric Johnson Mod Emeritus

    Joined:
    Nov 18, 2005
    Messages:
    5,732
    Loc:
    Central NYS
    It comes in a bottle. I think you can buy it at Home Depot, but if not, any plumbing supply house. You pour it in and it's silica, so it finds and stops up any small leaks. Professional plumbers say they never use it, but I have, and it worked fine. Takes a day or two to work.
  14. goosegunner

    goosegunner Minister of Fire

    Joined:
    Oct 15, 2009
    Messages:
    1,289
    Loc:
    WI
    It looks as though your boiler has stays on the side panels right?

    If so I would believe that it was that way from the factory, seems like it would be hard to move with stays in place.

    gg
  15. Floydian

    Floydian Feeling the Heat

    Joined:
    Dec 12, 2008
    Messages:
    437
    Loc:
    Southwestern VA
    Have you checked your water chemistry?

    Can you verify that your return water protection has been working correctly? I'm not thinking about condensation so much as boiler shock if return temps were really low.

    I tend to agree with gg that it probably came that way from the factory and I doubt boiler shock could cause that, though I don't know what boiler shock really is so.......

    Noah
  16. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    Stays? Do you mean those brackets that stick out? There is no band across the side of the boiler, those brackets are what the enamel casing screws to to hold it on.
  17. goosegunner

    goosegunner Minister of Fire

    Joined:
    Oct 15, 2009
    Messages:
    1,289
    Loc:
    WI
    In your second picture the round bump on the boiler that is right near the level bubble. They should be welded to inner and outer sheets of steel to maintain spacing.

    gg
  18. ozzie88

    ozzie88 Member

    Joined:
    May 13, 2011
    Messages:
    199
    Loc:
    maine
    Well I am not sure about that. In just a 10x10inch area there be 3000LB of force pusing out,think about it? about weight of pickup there.
  19. Eric Johnson

    Eric Johnson Mod Emeritus

    Joined:
    Nov 18, 2005
    Messages:
    5,732
    Loc:
    Central NYS
    GG and Ozzie make good points. If that spacer isn't welded to the inside plate, then it might be able to bulge under pressure. However, if that's the case, then it would probably leak water into the firebox, no? Not sure how these things are put together. I don't think there are corresponding lugs on the inside of the firebox, so perhaps they're just surface welded to the other side of the plate, instead of going through a hole in the plate and being welded inside the firebox. I'll have to look at mine when I get home.
  20. avc8130

    avc8130 Minister of Fire

    Joined:
    Dec 6, 2010
    Messages:
    1,000
    Loc:
    God's Gift to Gassification
    I would definitely start with a call to the dealer you bought it from. Just because they don't sell the brand any more, doesn't mean they shouldn't be motivated to help. You gave them quite a bit of money and they advertise on this forum. If they don't help, it would show very poorly for them.

    If that turns out to be a dead end, get on the phone with the importer.

    I wouldn't jump to repairing it yourself as that might void any chance of a warranty. If you are having small trouble with it now, you would certainly want to be covered for big trouble soon.

    ac
  21. henfruit

    henfruit Minister of Fire

    Joined:
    Nov 27, 2007
    Messages:
    712
    Loc:
    New Hampshire-Maine border
    I think you may want to read the specs sheet on an eko.It is written operating psi is 25 so if you have a 30 lb psi relief valve on it and are getting above the 25 psi spec that could be the explanation for the bulgeing.
  22. junkers

    junkers Member

    Joined:
    Feb 19, 2012
    Messages:
    10
    Loc:
    evropa
    boilers in Europe have a working pressure of 1 to 2bar Safeti valves are 2.5 bar

    a maximum working pressure for vigas is 3 bar
  23. henfruit

    henfruit Minister of Fire

    Joined:
    Nov 27, 2007
    Messages:
    712
    Loc:
    New Hampshire-Maine border
    or 43 psi
  24. stoney28

    stoney28 Member

    Joined:
    Oct 12, 2008
    Messages:
    59
    Loc:
    Northern NY
    I emailed New Horizon and they said they would cover the cost of the welder. They didn't say anything about the bulge though. I may bring it up again.

    GG - So you think maybe it was just made that way, then? I saw those little round things, but I didn't know what they were.