Chimney Height, 7ft above roof?

Chamel Posted By Chamel, Feb 3, 2013 at 4:20 PM

  1. Chamel

    Chamel
    Member 2.
    NULL
    

    Feb 3, 2013
    21
    3
    Loc:
    MA
    Hello, I just bought my first wood stove, a free standing Pacific Energy Vista. I read a lot about the2-3-10ft rule and still feel a bit confused about the height of chimney I should have. Right now I have 5ft of class-A double wall pipe that is extending from the roof, which meets the peak of my roof. The peak of the roof is about 8ft away from the chimney. Does this mean the chimney needs to rise an additionally 2ft above the peak? That would make 7ft of chimney extending from the roof? I know I would need a brace as well. Is that too much chimney to be sticking outside?

    Any help would be greatly appreciated. Thanks!

    Here's a little sketch for visual people:
     

    Attached Files:

  2. rijim

    rijim
    Member 2.
    NULL
    

    Jan 19, 2009
    210
    26
    Loc:
    RI
    No, that is what is required.
     
  3. RPK1

    RPK1
    Member 2.
    NULL
    

    Nov 24, 2008
    57
    1
    Loc:
    Eastern CT
    A chimney that is closer than 10ft to the ridge has to extend 2ft above the ridge.

    RPK
     
  4. Chamel

    Chamel
    Member 2.
    NULL
    

    Feb 3, 2013
    21
    3
    Loc:
    MA
    That's what I thought. Thanks for your help.
     
  5. ridemgis

    ridemgis
    Burning Hunk 2.
    NULL
    

    Jun 14, 2012
    234
    81
    Loc:
    South Kingstown, Rhode Island
    Is that a code or simply a general guideline? There are newer chimneys all over town here that don't meet the spec.
     
  6. Chamel

    Chamel
    Member 2.
    NULL
    

    Feb 3, 2013
    21
    3
    Loc:
    MA
    It's code I believe. I think as long as the chimney is 10ft away from the ridge you don't have to rise above it. Anything less than 10ft you would have to rise 2ft above it. Correct me if I'm wrong.

    I see a lot that don't meet that spec too.
     
  7. RPK1

    RPK1
    Member 2.
    NULL
    

    Nov 24, 2008
    57
    1
    Loc:
    Eastern CT
    Ct state Building Code for sure. I don't have the NFPA section but I am pretty sure it comes from there.

    RPK
     
  8. KaptJaq

    KaptJaq
    Minister of Fire 2.
    NULL
    

    Jan 31, 2011
    716
    341
    Loc:
    Long Island, NY
    An image of the 2-3-10 rule...

    chimney2.gif

    (Click image for full size)

    KaptJaq

     
  9. Jon1270

    Jon1270
    Minister of Fire 2.
    NULL
    

    Aug 25, 2012
    1,894
    1,057
    Loc:
    Pittsburgh, PA
    It has to be 2 feet above any part of the building that's within a 10' radius. If the penetration were near the bottom edge of a 12/12 pitched roof, it would have to stick up 12 feet.
     