    We bought a vacation place a few weeks ago, and I have a stove to install. Some brief searching hasn't shown me much for what to use to penetrate a metal roof. I found a silicone boot from Selkirk, but I'm not sure if that's what I need. We're taking a U-Haul full of crap in a couple of weeks, and I may be able to get the stove in, if I can gather what I need in time.

    It isn't corrugated, it looks like this. I think. I have only seen it once when it wasn't snow covered.

    metal-roof.jpg
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. topoftheriver

    topoftheriver
    Expand Collapse
    Member

    Joined:
    Jan 26, 2013
    Messages:
    238
    Likes Received:
    35
    Loc:
    Northeast
    If you're not sure, it would be wise to hire a professional so you don't damage the roofing. It is tricky to get the hole in the right spot.
     
    Collapse Signature Expand Signature
  3. jeff_t

    jeff_t
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    4,150
    Likes Received:
    1,098
    Loc:
    SE MI
    I have done two installs through shingled roofs, so I'm pretty familiar with the process. I'm just not sure how to seal up the metal roofing.
     
    Collapse Signature Expand Signature
  4. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Collapse Signature Expand Signature
    velvetfoot likes this.
  5. jeff_t

    jeff_t
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    4,150
    Likes Received:
    1,098
    Loc:
    SE MI
    Thanks.

    I can see this won't get done in an already sorta busy weekend. I think I better put it off until summer.
     
    Collapse Signature Expand Signature
  6. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Good idea, this is not a job you want to rush. Most importantly, remember that water wants to run downhill. Don't impede it by creating artificial dams of silicone where it isn't needed.
     
    Collapse Signature Expand Signature
  7. jeff_t

    jeff_t
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    4,150
    Likes Received:
    1,098
    Loc:
    SE MI
    Good point. There's not much pitch to begin with.

    The previous owners left us with 68% in the 500 gal pig ;). No hurry, I guess. Probably should buy some wood, though.
     
    Collapse Signature Expand Signature
  8. Leroy_B

    Leroy_B
    Expand Collapse
    Member

    Joined:
    Dec 23, 2010
    Messages:
    62
    Likes Received:
    20
    Loc:
    Southern N.H.
    I'm going to follow this thread closely. I also wondered about a chimney flashing for a metal roof and how the install is done without any water damming up.
     
  9. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,008
    Likes Received:
    1,393
    Loc:
    Indiana
    I know some people use the silicone flashings with success, but I often find them leaking. In addition to the risk of leaking, they offer NO support for the chimney like a metal flashing offers.
    Anytime we do a metal roof install we use this one from ICC. It offers a permanent seal, it installs similar to a shingle type flashing, by tucking under the metal on the top side.

    Here is the flashing to use: http://www.icc-rsf.com/main.php?t=chem_produits&i=95&l=en
     
    Collapse Signature Expand Signature
  10. Treacherous

    Treacherous
    Expand Collapse
    Minister of Fire

    Joined:
    May 13, 2010
    Messages:
    995
    Likes Received:
    118
    Loc:
    WA state
    I have this one. No complaints here.

     
    Collapse Signature Expand Signature
  11. jeff_t

    jeff_t
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    4,150
    Likes Received:
    1,098
    Loc:
    SE MI
    Maybe we should think about tearing the brick chimney down and go thru the wall. There is a ceiling support in place from a previous metal chimney, but they covered the hole when they put the new roof on. The exit point has to be almost at the peak. I'll have get in the attic and take a look.

    The hearth that is there has a TV on it now :rolleyes:

    2013-01-19_16-11-59_811.jpg
     
    Collapse Signature Expand Signature
  12. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,008
    Likes Received:
    1,393
    Loc:
    Indiana
    Can you re-line the chimney thats in place?
     
    Collapse Signature Expand Signature
  13. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Good advice. Do you have any roof shots of an install?
     
    Collapse Signature Expand Signature
  14. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,008
    Likes Received:
    1,393
    Loc:
    Indiana
    No, I usually take pics of the stove, but never thought to take a pic of the chimney.
    I do a few a month through metal, I'll get a pic next time.
     
    Collapse Signature Expand Signature
  15. Bret Chase

    Bret Chase
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    870
    Likes Received:
    251
    Loc:
    Maine
    flashing a metal chimney through a metal roof (screwdown or standing seam) isn't that big of a deal... if the hole stays in the flat and doesn't go through a rib. If it's a standing seam roof is is generally better to use the silicone boot and figure out a different way to secure the top of the chimney, as a SSR is only restrained at the bottom, and grows toward the peak as it heats up. With a screwdown it is also generally easier to use the silicone boot... though I have done a couple with a shingle type boot, but it requires cutting the panel....

    if your hole transitions a seam in a SSR..... it becomes an ugly, ugly nightmare... the worst one I had to do involved 2 12" metalbestos chimneys that were less than 2' apart.... it took me almost 2 days to get it tight...
     
    Collapse Signature Expand Signature
  16. charly

    charly
    Expand Collapse
    Guest

    When I went through my corrugated metal roof, I bought a stove pipe laser level that fits inside the top of the stove pipe or your wood stove and projects a laser dot right at the center point on the roof or what ever you are going through.. Was dead nuts on..scribed a circle after marking the dot and it was dead on plumb. I wound up using the silicone boot flashing kit..So far no leaks...
     
  17. eclecticcottage

    eclecticcottage
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 7, 2011
    Messages:
    1,787
    Likes Received:
    342
    Loc:
    WNY
    Just watching...we are thinking of doing a standing seam roof eventually, and we'll need to deal with this then.
     
    Collapse Signature Expand Signature
  18. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Finally found a shot of the ICC flashing. I knew I had it sitting somewhere in my desktop junk.This is at the ridge, but the bottom detail is good. The storm collar has not been installed yet. Note that the sealant is only under the side flanges. The bottom is left unsealed for drainage.

    ICC_metal_roof_flashing.jpg
     
    Collapse Signature Expand Signature
    jeff_t likes this.
  19. chimneylinerjames

    chimneylinerjames
    Expand Collapse
    Feeling the Heat

    Joined:
    Nov 26, 2012
    Messages:
    389
    Likes Received:
    51
    I would see what it would take to line the brick chimney. If its not in use, I would try to use the chimney that's already there. Just install a liner with insulation and your set.
     
    Collapse Signature Expand Signature
  20. Bret Chase

    Bret Chase
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    870
    Likes Received:
    251
    Loc:
    Maine
    the bottom detail isn't great.... is that a foam closure on the bottom, or was the metal cut to fit?
     
    Collapse Signature Expand Signature
  21. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    I think he wants to get the stove more centrally located with a taller, straight up flue. The brick chimney is pretty short. Add a couple 90º turns in the smoke path and it is going to draw poorly.
     
    Collapse Signature Expand Signature
  22. webby3650

    webby3650
    Expand Collapse
    Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    6,008
    Likes Received:
    1,393
    Loc:
    Indiana
    It's cut to fit. I seal the bottom edge though. The customer can see daylight and they don't like it.
    And I don't think there would really be any drainage allowed due to the size of the hole only inches away from the tail of the flashing. On a shingles roof it makes good sense, but here, I would rather seal it.
     
    Collapse Signature Expand Signature
  23. Bret Chase

    Bret Chase
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    870
    Likes Received:
    251
    Loc:
    Maine

    I seal it when I install them in a metal roof... I don't care what the customer "wants"... They never seem to like the "I told you so..." I don't want the callback for the chimney leaking due to wind driven rain, or the ice damn that *always* happens just down hill of the chimney...
     
    Collapse Signature Expand Signature
  24. charly

    charly
    Expand Collapse
    Guest

    That's great if you can tuck the top under the ridge cap,, but that not always the case.
     
  25. Lumber-Jack

    Lumber-Jack
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 29, 2008
    Messages:
    2,003
    Likes Received:
    932
    Loc:
    Beautiful British Columbia
    My roof install was very much like this except the chimney came out a little lower down from the ridge cap. All you have to do is cut another piece of the same type of metal roofing and install it so the lower part over-laps the chimney flashing and the top goes under the ridge. Done!
     