    Has anyone ever disconnected the OAK from the're stove and seen any differences in Pellet consumption.. less? more/?
    or other operation differences? pertaining most to users who might not have really needed an Open air setup due to drafty or not well insulated house?
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. bob bare

    bob bare
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 31, 2013
    Messages:
    1,358
    Likes Received:
    193
    Loc:
    park county montana
    Well this ought to stir things up.Cold air is less efficient burning,preheated intake air becoming more commonplace.Chickenfarmer can explain it better,but cold air takes heat to burn better.However as pellet stoves are not that efficient,do not think you would see a big difference except in long term sub zero.If stoves were more efficient you would see a big difference.
     
    Collapse Signature Expand Signature
  3. bob bare

    bob bare
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 31, 2013
    Messages:
    1,358
    Likes Received:
    193
    Loc:
    park county montana
    Sorry it is chickenman,not chickenfarmer.He builds,mods stoves.
     
    Collapse Signature Expand Signature
  4. Tonyray

    Tonyray
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 11, 2013
    Messages:
    2,107
    Likes Received:
    576
    Loc:
    Bucks County,Pa /North of Phila Eagles
    have read a few post where some have disconnected Oak from the back of the stove and just let it lay on the floor behind the stove...
    but the thread is closed so no input as to pellet consumption or operation differences..
    that said, with it on the floor I would assume cold outside air would be flowing thru it but being pulled into the stove but NOT as direct as when hooked up?
    either way still don;t know if this is good or bad to do this.
     
    Collapse Signature Expand Signature
  5. Polar Bear

    Polar Bear
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 4, 2014
    Messages:
    435
    Likes Received:
    118
    Loc:
    Sudbury, ON, Canada
    You would think if the power went out the fumes would seep out the OAK since there's no vertical draw...
     
    Collapse Signature Expand Signature
  6. alternativeheat

    alternativeheat
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 19, 2013
    Messages:
    2,912
    Likes Received:
    816
    Loc:
    Cape Cod, Ma.
    That depends on the exhaust arrangement according to Harman. Put in at least 4' vertical vent. I have that covered with 23 ' of vertical 4" vent ! We lost power over the winter, the flame just went to a fireplace flame till the pellets in the pot burned out. No oak, no smoke in the house.
     
    Collapse Signature Expand Signature
  7. #7 Don2222, May 6, 2014
    Last edited: May 6, 2014
    Don2222

    Don2222
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 1, 2010
    Messages:
    7,767
    Likes Received:
    459
    Loc:
    Salem NH
    X2, I agree 100% but I have pre-heated OAK air from the outside using Selkirk DT. There is no better more efficient solution by far!

    Click pic to Enlarge
     

    Attached Files:

    Collapse Signature Expand Signature
  8. stoveguy2esw

    stoveguy2esw
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 14, 2006
    Messages:
    6,163
    Likes Received:
    1,087
    Loc:
    madison hgts. va
    one would have to look at the amount of air drawn by the stove , then think about paying to heat that air which will be used for combustion and dumped out the exhaust. I've found that houses (especially not too tight ones) which would not necessarily need and OAK for negation of pressure issues tend to be far less drafty when an OAK is installed

    most exhaust blowers are rated at up to 135CFM that's a lot of air (granted they aren't likely pulling that much but its not a trivial amount either). that air has to be replaced somehow, so if no OAK is used the air is simply going to be replaced through the nooks and crannies making the house harder IMHO to heat as this air can be drawn in through leaks farther from the stove.
    not having the time nor the ambition to study this formally I do have my OPINION that the loss of top end combustion achieved with air heated up the extra 50-70F is going to less noticeable than the heat loss generated by cold air intrusion from the negative pressure buildup from using house air.

    just my 2 cents.

    note: we at ESW feel strongly enough about it that we REQUIRE an OAK n our installation manual and to that extent we include one with every pellet stove we ship.
     
    Collapse Signature Expand Signature
    UMainah, chickenman and mithesaint like this.
  9. bob bare

    bob bare
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 31, 2013
    Messages:
    1,358
    Likes Received:
    193
    Loc:
    park county montana
    That's why I did not touch on "to have or not",only the difference of preheated air.But if you have a stove that the intake air is not sealed(they still make them)then whenever stove is off cold air migrates into house,possibly negating any savings before.Especially true in shoulder seasons when stove may be off a few days in a row,or part of the day.Different stoves,different installs,all has to be looked at.
     
    Collapse Signature Expand Signature
  10. Don2222

    Don2222
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 1, 2010
    Messages:
    7,767
    Likes Received:
    459
    Loc:
    Salem NH
    X2, The harman P-Series do not have any half baked OAKs. In other words, the air inlet pipe goes to a sealed burn pot with no prior opennings in the stove. Also there is a flapper valve to keep the cold air out when the stove is off! Those are important features to consider in a stove. IMHO
     
    Collapse Signature Expand Signature
  11. doghouse

    doghouse
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 9, 2008
    Messages:
    353
    Likes Received:
    53
    Loc:
    maine
    Words to live by. Thank you, Mike
     
    Collapse Signature Expand Signature
  12. BrotherBart

    BrotherBart
    Expand Collapse
    Hearth.com LLC Mid-Atlantic Division
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    32,380
    Likes Received:
    9,607
    Loc:
    Northern Virginia
    Why I have always figured that 500 pound wood stove in my living room tied to a stainless liner up to the cap is a huge heat sink when it isn't burning. Not to mention the draft from the chimney since the air inlets can't even be totally closed.

    Small thing in the greater scheme of things though.
     
    Collapse Signature Expand Signature
  13. railfanron

    railfanron
    Expand Collapse
    Feeling the Heat

    Joined:
    Nov 2, 2013
    Messages:
    253
    Likes Received:
    41
    Loc:
    Perry MI
    I just would like to add this. Without an OAK the air in a 1200 sq. ft. house is sent up the chimney in about 90 minutes of operation. I can't imagine how leaving it disconnected can actually save money.
    Ron
     
    Collapse Signature Expand Signature
  14. moey

    moey
    Expand Collapse
    Minister of Fire

    Joined:
    Jul 12, 2012
    Messages:
    1,323
    Likes Received:
    325
    Loc:
    Southern Maine
    What type of differential did you see in how much the air was warmed. For example if you had 5 ft of pipe and it was 0C outside what temperature was your intake air? I know there are lots of variables other then just ft of pipe. Im just curious approximately what increase in temp you saw.
     
    Collapse Signature Expand Signature
  15. railfanron

    railfanron
    Expand Collapse
    Feeling the Heat

    Joined:
    Nov 2, 2013
    Messages:
    253
    Likes Received:
    41
    Loc:
    Perry MI
    I'm wondering how much benefit you get from warm air verses cold. Warm air takes less temperature out of the combustion but cold air is denser so there is more Oxygen in it for the combustion. I bet the difference is actually very little but I really have no facts to back this up.
    Ron
     
    Collapse Signature Expand Signature
  16. spottedbat

    spottedbat
    Expand Collapse
    New Member

    Joined:
    May 8, 2014
    Messages:
    3
    Likes Received:
    0
    Loc:
    Farmington, ME
    What pellet stoves do not require OAK?

    Mike, i talked to you today about installing a pellet stove with the duraflex up my chimney. I was all excited and told my husband its all set- know exactly what we need blah blah. when i mentioned the OAK through the wall he was totally against it and wants a pellet stove that wont need it. ARG! i have been researching this long enough. Can you and anyone one else direct me to what brands "suggest" using one but it isnt necessary to operate with, harmon maybe? I thought i would have such a deal with the englander from amfm but now i can't have that brand because someone thinks its an eyesore. I have good airflow asw this house is not very insulated.
     
  17. doghouse

    doghouse
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 9, 2008
    Messages:
    353
    Likes Received:
    53
    Loc:
    maine
    Try this: http://www.selkirkcorp.com/Selkirk/Product.aspx?id=7428
     
    Collapse Signature Expand Signature
  18. spottedbat

    spottedbat
    Expand Collapse
    New Member

    Joined:
    May 8, 2014
    Messages:
    3
    Likes Received:
    0
    Loc:
    Farmington, ME
    i like the idea of selkirk direct temp but it is not for in the chimney. it would be great if we decide to go through the house wall, but that is after we run it for a year and decide its worth making a hole in the wall! Anyone have a stove that does not require having the air kit?
     
  19. stoveguy2esw

    stoveguy2esw
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 14, 2006
    Messages:
    6,163
    Likes Received:
    1,087
    Loc:
    madison hgts. va
    this isn't a factor with our stoves (or most epa cert pellet stoves) 35-1 requirement does not have to be met with cert stoves so we can take it under that threshold and routinely do.
     
    Collapse Signature Expand Signature
  20. stoveguy2esw

    stoveguy2esw
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 14, 2006
    Messages:
    6,163
    Likes Received:
    1,087
    Loc:
    madison hgts. va

    more manufacturers are doing so , the "handwriting is on the wall" has been for some time. first it was certain states such as Washington disallowing exempt units, now its being pushed on a national scale. we've been producing certified pellet stoves for at least the last 15 years and have absolutely no interest in any new designs without certifications , wouldn't be anywhere to sell them.

    IMHO this is one area where so far the industry and the government have managed to reach a modicum of symbiosis in the balance between regulation and demand. as long as progress is made in a deliberate manner which allows the industry to adjust to he changing regs we can do this. however if regulation becomes too draconian too quickly it will seriously harm the hearth industry.
     
    Collapse Signature Expand Signature
    chickenman likes this.
  21. spottedbat

    spottedbat
    Expand Collapse
    New Member

    Joined:
    May 8, 2014
    Messages:
    3
    Likes Received:
    0
    Loc:
    Farmington, ME
    We were thinking of getting a pellet stove to put where our broken jotul woodstove was and run the exhaust up through the chimney with a duraflex. Since it is a single flue and would need to have an air intake tube running through something like a wall, that's quite an intrusive install and i would need to rearrange our living space and because of that air tube we are calling it quits. Also there seems to be quite a learning curve for new users, and it sounds like it takes more to run this thing than a woodstove. After many grueling hours of research we are going to pass up the pellet stove and stick to getting our woodstove refurbished. I guess our house just isn't right for the set up of a pellet stove, well at least one that wouldnt cost me thousands. Maybe in the future, especially if Selkirk makes a direct temp for a chimney not associated with a fireplace. Thanks for everyone's help in answering my questions on this very informative forum.
     
  22. UMainah

    UMainah
    Expand Collapse
    Member

    Joined:
    Jan 4, 2012
    Messages:
    197
    Likes Received:
    21
    Loc:
    Bangor, ME
    You can use Selkirk DT in a chimney. You'll need a metal or masonry chimney conversion kit. It's an attractive option.
     
    Collapse Signature Expand Signature
  23. batchman

    batchman
    Expand Collapse
    Burning Hunk

    Joined:
    Oct 29, 2013
    Messages:
    165
    Likes Received:
    32
    Loc:
    Backwoods MA
    What you're running into is the same thing I found, Pellet hardware is not often a direct replacement for cordwood. I was in the same boat as the only viable place I had for a pellet stove was to replace a cordwood stove that would not draft.

    I think it's proving elusive as it's not "off the shelf", but I would think if you had venting in the cap plate at the top of your chimney, and the exhaust extended above the top by a couple of feet, you could probably use the "indoor" portion of the Selkirk vent and then draw your intake air from the void in the masonry chimney.

    FWIW my Enviro Maxx does not require outside air if you're not in a very tight or mobile home, and in fact I am finding it uses more indoor air than I would like. Perhaps others in their line may work.

    Good luck either way!
    - Jeff
     