EKO 40 Install and Pump Selection
mhearts
31
Syracuse NY
I am installing a new EKO 40 and am running 160 total feet (80ft out and 80ft back) of 1 1/4 copper to an existing boiler. I wonder what pump others are using with the EKO 40 . I have spoke to a local guy who has run an outdoor boiler for several years and he told me a two pump setup is best. One on the return side and one on the supply side is better than one big pump. I am considering a Grundfos UPS 15-58FC . Anyone else using this pump?
What pump are others using with their EKO 40 when hooked directy to an existing boilier ? Also give distance and pipe size. And comment on ability to remove heat generated by the EKO 40
Thank you
If that is a 40KW boiler X 3.41= 136,000 BTU/hr . At 70% efficiency 95,000 output.
You are talking about moving about a 95,000 BTU/ hr load. At a 20 degree delta t you will need to move 9.5 gpm. 160 feet of 1 " copper would be a pressure drop of 4.5 feet per 100 feet of tube at 180F water. Throw in some fittings and valves and call it 9.5 gpm at 8 feet of head. A Grundfos 15-58 would handle that.
Are you flowing through any other heat exchangers, boilers, devices? If so you need to know the pressure drop through them. But unless you have a high pressure drop in something along the circuit that 15-58 should be plenty.
I wish I understood all that.....
What would happen if you installed a pump that was too big? alternatively, what if you picked one that was too small? Is there much margin of error when choosing pump sizes or close enough good enough? Better to be too big rather than too small?
circulator pumps (circs) come in a lot of different sizes and styles. To size a circ you need to know how how many gallons per minute GPM you need to move and the system resistence (head).
Manufacturers will often give you this info for the boiler you chose. A rule of thumb is you need to move 1 gpm for every thousand BTUs.
I think nofo may be correct about wood boiler ratings being output not input. My EKO 40 shows a "power range" of 8-40, then states 85% efficiency. I'm not sure if the output is with or without the efficiency % figured?? Gas, oil,and LP boilers are typically rated as input BTU/hr.
Let say is does have an output of 40KW or 136,000 btu/ hr. In that case you need to flow, or move 13.6 GPM. that is the first number to use when sizing the circ.
The next is resistence to flow or "head" Every device, pipe, fitting, valve, etc in the piping circuit has resistence to flow. Again many boiler manufactures will give you a "head" number at different flow rates.
Wood boilers are typically fairly wide open vessels with little flow resistence.
Pipe also has resistence to flow at various flow rates. This can be determined by the size, length, and flow rate through the pipe.
B&G;has a free download System Sizer at their website that will give you this data.
Once you know the head through all the components in the piping system, you can select a circ by looking at pump curve charts.
This one is for the Grundfos 15-58 3 speed I mentioned above, and a Grundfos one that covers a selection of circs.
If you use my "guesstimate' of 8 feet of head, and now 13.6 gpm follow the 8 feet of head line over the 13.6 gpm line. this circ is a bit small for the job. IF the system has 6 feet of head, then this circ would be perfect.
You want to shoot for the "knee" or middle 1/3 of the pump curve. Never size a circ at the very top or bottom of the curve.
Too large of a circ will use excessive energy, possibly add too much head energy. Excessive velocity in the pipe and components will cause noise, wear, and the circ may overheat and not last very long.
I sized the pressure drop "head" for your piping as you described, now you need to figure the head for the rest of your components to select the correct circ.
As luck would have it most circ manufacturers now offer 3 speed circs. This makes it much easier to match the circ to the job without shopping for the "exact" one.
In your case the 3 speed 26-99 might be a better choice. It will depend on the variable you have yet to determine. Or a wild guess based on experience :)
Great tutorial on circulator sizing. Should go into the wiki. It will definitely be going in my hydronics folder. Thanks HR.
Will
Thanks for looking this over.
I agree we have to flow 13.6 gpm thru the system to remove the BTU's generated.
Determining head needs to be clarified. Please note that I said I was using 1 1/4 pipe and not 1 inch pipe. This has quite an influence. The friction loss of water in a 1 1/4 pipe, while flowing 13.6 gpm (when I look it up) is 1.5 ft of head/100ft . This is 2.5 ft of head loss for the 160 ft run. Now adding in the internal friction loss of the EKO 40 and the friction loss of the the direct connection to the existing boiler and I am going to assume we stay below 6 ft of head.
So as long as 1 1/4 pipe is being used the Grundfos 15-58 may just be the perfect pump match for the EKO 40!!! assuming around 6 ft of head.
Are any other EKO 40 users running a 15-58 multi-speed pump?
Right you are. I was trying to get you into a smaller diameter pipe when I assumed a lower flow rate. The difference between 1 and 1-1/4 copper for that distance will be 300 bucks or more plus the insulation cost difference.
But as you see by running the numbers the 1-1/4 will be a better choice, and keep you in a 78W less expensive circ.
hr
