Englander into a masonry chimney

jssls Posted By jssls, Jul 17, 2008 at 7:25 PM

Thread Status:
Not open for further replies.
  1. jssls

    jssls
    New Member 2.
    NULL
    

    Jul 17, 2008
    8
    0
    Loc:
    Central Maine
    I am looking at venting a Englander 25-pdvc into a masonry chimney. Total vent distance would be about 24'. Can I vent directly into my chimney or do I need a liner?
     
  2. stoveguy2esw

    stoveguy2esw
    Minister of Fire 2.
    NULL
    

    Nov 14, 2006
    6,171
    1,089
    Loc:
    madison hgts. va

    whats the flue diameter? answer will depend on that.
     
  3. jssls

    jssls
    New Member 2.
    NULL
    

    Jul 17, 2008
    8
    0
    Loc:
    Central Maine
    The chimney is a standard tile lined chimney approximately 8" square. I would have to climb up the get the exact measurement. It has an 8" thimble also.
     
  4. stoveguy2esw

    stoveguy2esw
    Minister of Fire 2.
    NULL
    

    Nov 14, 2006
    6,171
    1,089
    Loc:
    madison hgts. va
    that length and diameter , you should probably install a liner, with that big a flue its gonna be hard to maintain flue temps. i'd be more comfortable with a 6" but 8 inch or bigger (with an 8" thimble you will be 8 or bigger) especially with 24 ft of flue , i just dont see it working as well as it would with a 4" liner.
     
  5. jssls

    jssls
    New Member 2.
    NULL
    

    Jul 17, 2008
    8
    0
    Loc:
    Central Maine
    Thanks for the info. Is it correct to assume the same would apply to a 25-PDVC model as well? By the way, what is the BTU output of the 25-PDV and the 25-PDVC? I might need to change my plans due to dimensional issues. Thanks.
     
  6. stoveguy2esw

    stoveguy2esw
    Minister of Fire 2.
    NULL
    

    Nov 14, 2006
    6,171
    1,089
    Loc:
    madison hgts. va
    yes, while a 6" flue at that length may have worked well, an 8X8 is just too big for either unit.
     
  7. slls

    slls
    Minister of Fire 2.
    NULL
    

    Jun 9, 2008
    1,497
    53
    Loc:
    central maine Lat 45
    Installation manuals say no more than 6 inches round or 28 square inches. Even 6 inch square would be too large.
     
  8. stoveguy2esw

    stoveguy2esw
    Minister of Fire 2.
    NULL
    

    Nov 14, 2006
    6,171
    1,089
    Loc:
    madison hgts. va
    yeah , youre right , i was saying 6 Inch but didnt specify round , which is what mine is hooked to at 14 ft. it will work with that as it has for 3 winters in my hookup. actually it probably would in a single story chimney with square but at 24 ft it would be hard to keep the flue tiles hot. this could lead to creosote buildup as moisture present could liquify. 8X8 is definately too big.
     