Harman P68 will not shut off after stove cools down.

Post in 'The Pellet Mill - Pellet and Multifuel Stoves' started by garyb009, Nov 15, 2012.

  1. garyb009

    garyb009 New Member

    Joined:
    Dec 10, 2010
    Messages:
    7
    Loc:
    gainesville, va
    I was having trouble with my circuit board so I replaced it. Now my Combustion blower will not shut off. Even after I turn the unit off it continues to run even after the stove gets cold. I have to pull the plug to get it to stop. I called Harman and got the correct dipswitch settings prior to installing the new board. So I don't think that's the problem. Does anyone have any idea why this may be happening? Thanks for any help you can give me.

    Helpful Sponsor Ads!





  2. silverfox103

    silverfox103 Feeling the Heat

    Joined:
    Oct 4, 2011
    Messages:
    465
    Loc:
    Littleton, NH
    That is a common problem with that stove. I had it and they put in a revised board. Not 100% sure, but I believe I ended up shutting it off by using the feed rate control.

    Tom C.
  3. Bioburner

    Bioburner Minister of Fire

    Joined:
    Aug 4, 2012
    Messages:
    2,899
    Loc:
    West central Mn
    Exaust fans on Harmans can run for up to five hours after shut down per the manual.
  4. mepellet

    mepellet Minister of Fire

    Joined:
    Aug 10, 2011
    Messages:
    1,846
    Loc:
    Central ME
    When you say the combustion blower continues to run even after the stove gets cold, how cold are you talking? How long after you turn the stove off do you end up pulling the plug?
  5. garyb009

    garyb009 New Member

    Joined:
    Dec 10, 2010
    Messages:
    7
    Loc:
    gainesville, va
    I would say a good 2-3 hours. Now that i see what BIOBURNER has to say, maybe it is normal. I will have to take note on my next burn. I will get it good and hot and than stop the feed and see how long it runs. I know last year the combustion blower would shut off once the stove was cold to touch.
  6. garyb009

    garyb009 New Member

    Joined:
    Dec 10, 2010
    Messages:
    7
    Loc:
    gainesville, va
    Thanks Tom- seems to me that once I shut the stove off, which stops the auger, the blower should shut off once it cooled down without having to adjust the feed rate.
  7. TheMightyMoe

    TheMightyMoe Minister of Fire

    Joined:
    Aug 2, 2012
    Messages:
    544
    Loc:
    Fairbanks, Alaska.
  8. rickwai

    rickwai Feeling the Heat

    Joined:
    Nov 1, 2011
    Messages:
    289
    Loc:
    ohio
    Make sure igniter is not sticking on. After shutdown and stove feels cool and unit is still running open door and put hand near burn pot and see if it is hot. I have seen this happen.
  9. Bioburner

    Bioburner Minister of Fire

    Joined:
    Aug 4, 2012
    Messages:
    2,899
    Loc:
    West central Mn
    Page 25 of my manual, Trouble shooting, Combustion blower runs after shutdown, "This is a normal function. The combustion blower will run for 5 hours after the stove is completely cool." Pain in the a-- because if your oaking things can get very cold only to crank up and reheat the unit wasting energy- pellets. I run in manual mode to keep stove from cycling when it's a bit warmer.
  10. garyb009

    garyb009 New Member

    Joined:
    Dec 10, 2010
    Messages:
    7
    Loc:
    gainesville, va
    Here is what happened today. I set my room temp to 70 degrees, when it reached that general temp it stopped burning pellets andthe stove cooled down. I let the combustion blower run for a good 6 or 7 hours before I pulled the plug to stop it. Also here is another issue, the stove should have fed pellets into the burn pot and reignite because the room temp dropped to probably 60 degrees and it didn't.
  11. Bioburner

    Bioburner Minister of Fire

    Joined:
    Aug 4, 2012
    Messages:
    2,899
    Loc:
    West central Mn
    If you just replaced board it doesn't rule out getting another bum board. One reason I jumped on getting a second like kind stove. A quick swap out of a working unit will hopefully keep my headaches to a minimum. Predicting a colder than normal winter here with normal snow of about 50". Good luck
  12. Lousyweather

    Lousyweather Guest

    correct dip switch settings on the new board?
  13. garyb009

    garyb009 New Member

    Joined:
    Dec 10, 2010
    Messages:
    7
    Loc:
    gainesville, va
    Harman gave me the correct dippswitch settings. I called them when I installed the board. Great customer service btw.
  14. Lousyweather

    Lousyweather Guest

    yea, pretty important to get the right switch settings based upon the series of board you have......especially number 5
  15. Heat Slinger

    Heat Slinger New Member

    Joined:
    Sep 5, 2013
    Messages:
    18
    Loc:
    NB, Canada
    Did you ever resolve the blower issue with your P68? Is it normal for it to run for hours after you turn it off?
  16. imacman

    imacman Guest

    What??? That's just plain ridiculous. Can't be true though..... given what they cost, they can't possibly have ANY flaws.
    :rolleyes:
  17. MSmith66

    MSmith66 Feeling the Heat

    Joined:
    Feb 5, 2008
    Messages:
    350
    Loc:
    Central NY
    Just had the same thing with a customers stove, looked at the ESP probe and it was turned at a 90 degree angle. Replaced it and the stove was fine.