Help! We have drips of goo running down on outside of double wall onto Blaze King stove.

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

RCNIELSONRANCH

New Member
Nov 9, 2023
1
Juliaetta, ID
Help! We have drips of goo running down both sides now, on outside of the double wall pipe where it then piles up in a hard bubble (I had scraped off just prior to pict) onto Blaze King stove. It smell & looks like creosote. Some background & info: The stove (we have the King model for 3200 sf home) & double wall pipe going from stove to ceiling are only about 2 years old. Everything from the double wall up: the triple wall pipe, ceiling box etc, were all installed in 2006. Only issue we had when putting in the new stove & double walled pipe was finding the adapter between the double & triple wall (during Covid). Dealer gave us a very small section of single wall that slips inside & adapts the double wall to the triple wall pipe. Once it is slid inside those, only about an inch of the single wall can be seen from the outside. Everything seems to vent & work well. We are very careful to clean our pipes twice a year & maintain the woodstove regularly as is suggested by manufacturer. We usually burn dried (fresh cut each year but, taken off our logdeck of logs that we had delivered & stacked on our property a few years ago now) redfir, tamarack & mixed with some locust we cut around our property (grows like mad around here) & give time to dry out prior to burning. Because it is about 15' from from stove to ceiling box, we were told by Blaze King dealer that it was a good idea to open up the stove & let it burn hotter for about half hour each day to help warm up the pipe to keep creosote from building up so fast in the pipes, which we do. We are disaapointed & worried qhen we started seeing some creosote goo running down the outside of the pipes. Hoping you guys may have an idea of what may be causing the dripping we are seeing so we can fix it. I included pictures of our set up to help. Note: the chimney on roof stand alot taller but, I was taling that picture from the ground. Any ideas you have to help us fix this issue qould be greatly appreciated!

20231109_085556.jpg 20231109_085614.jpg 20231109_085647.jpg
 
When installed properly and there are no screw holes or other leaks, the creosote should run back down and into the stove for destruction. For every level of moisture content in a fuel load, there is a minimum burn rate at which the stove can be operated in order to deal with combustion moisture.

Yes, you should operate the appliance on high periodically, but not with the bypass open. Instead, the high burn recommendation is to reduce accumulation within the firebox.

When you load the stove, you should perhaps run it on a higher burn rate each time for 30 minutes, dealing with whatever level of moisture in the fuel at higher operating temperatures. If you go to bed at 9:00 pm. do not load the stove at 8:50, turn it down and go off to bed. Instead load it full at 8:00 p.m., turn the stove up to a higher burn rate for 30+ minutes. Then at 9:00 p.m., when you are ready for bed, turn the stove down.

BKVP
 
  • Like
Reactions: Highbeam
The cap looks odd. Was the triple-wall chimney pre-existing or new DuraPlus chimney? If the chimney pipe is old, air-cooled triple wall it is not code and no longer allowed for wood stove use.

Can't see from the chimney picture, but I suspect something was done wrong up there. The storm collar sealing is a suspect.
 
If done properly, no liquid smoke will leave the pipe. You have a pipefitting problem and that odd piece of single wall that you mention along with mismatched parts from different decades and maybe different brands makes me think the transition from new double wall to your old ceiling box is the most likely place.

This is not normal, you shouldn't have to tolerate it. What a mess all over your expensive 15' interior run.